Help needed please

C

Chris Autey

Hello everyone I'm new here and currently stuck with some homework!

Basically the question is:
What is the In for a BS 88 fuse from table 41.2 with an Ib of 15A?

Ive found the tables in my regs book but can't make head nor tale of it could somebody kindly explain to me how to do this in simple terms so I can understand lol cos its doing my head in not knowing what's going off and I feel I'm missing the obvious.

many thanks
 
Well (Ib) is your design current of 15A now you need a protective device (In) equal or greater , if you go back to the table 41.2 what size of protective device is equal or greater
 
There are 4 above 15a so I could use any of the four or would they be a preference? Forgive me if I sound thick lol
 
You would normally pick the next size available , but you can use any equal or greater but then you have to consider/use bigger cables ..
 
Ha many thanks! I am finding myself thinking that stuff is harder than it actually is on my electrical journey when infact most of it really is just straight forward lol...

Thanks again
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Chris Autey,
Last reply from
i=p/u,
Replies
9
Views
921

Advert

Back
Top