Bit of help needed please
A single phase load of 13a is supplied via a 15a bs 1361 fuse using single core 70c thermoplastic copper cables installed to method 4 (ref method b) the rating fator for grouping is 0.7 and for the ambient tem 0.87, and overload protection is to be provuded. the minimum acceptale size cale would be?
Can someone please explain how this is caculated.
Q2 which of the following statments regarding exhibitions,shows and stands is incorrect?
A- all socket outlets not excceeding 32a shall be protcted by an rcd
B- the norminal supply v shall not exceed 230/400v a.c
C- all electric motors shall have means of isolation.
D- signs shall be construceted of materials having an adequate heat resistance.
I thought the answer was d as i could not find it in the regs but i was told the answer is c but 711.55.41 states where an electric motor gives rise to a hazard the motor shall be provided with an effective means of isolation on all ploes and such means shall be adjacent to the motor which it controls. so which one is right?
Q3 the space under a bath, unless accessible only with a tool is considered to be in zone?
A-0
B-1
C-2
D-3
I understand that the space under a bath tub or shower basin is zone 1 and if its only accessible with a tool it is considered to be outside of the zone. is this question asking me which zone the space under a bath is with or without the use of a tool?
Thank you for those who take take the time to read my questions and answer them much appreciated
A single phase load of 13a is supplied via a 15a bs 1361 fuse using single core 70c thermoplastic copper cables installed to method 4 (ref method b) the rating fator for grouping is 0.7 and for the ambient tem 0.87, and overload protection is to be provuded. the minimum acceptale size cale would be?
Can someone please explain how this is caculated.
Q2 which of the following statments regarding exhibitions,shows and stands is incorrect?
A- all socket outlets not excceeding 32a shall be protcted by an rcd
B- the norminal supply v shall not exceed 230/400v a.c
C- all electric motors shall have means of isolation.
D- signs shall be construceted of materials having an adequate heat resistance.
I thought the answer was d as i could not find it in the regs but i was told the answer is c but 711.55.41 states where an electric motor gives rise to a hazard the motor shall be provided with an effective means of isolation on all ploes and such means shall be adjacent to the motor which it controls. so which one is right?
Q3 the space under a bath, unless accessible only with a tool is considered to be in zone?
A-0
B-1
C-2
D-3
I understand that the space under a bath tub or shower basin is zone 1 and if its only accessible with a tool it is considered to be outside of the zone. is this question asking me which zone the space under a bath is with or without the use of a tool?
Thank you for those who take take the time to read my questions and answer them much appreciated