Help needed with an RCD question | Page 2 | on ElectriciansForums

Discuss Help needed with an RCD question in the UK Electrical Forum area at ElectriciansForums.net

V

vickery1971

Hello again, as usual I need some advice from the learned amongst us. I went to a job today with the customer saying he was reading a book and the RCD tripped. When I got there he had sussed that it was the RFC in his flat and had turned that circuit off. I unplugged all appliances and it was still tripping. I then began to check the circuit out to check for a faulty socket or water ingress. To cut a long story short I ended up sussing that the RCD stays on until it is under load, it seems that the oven circuit (on its own circuit and working fine with the oven) but if you plug any appliance into the cooker switch it trips as soon as there is a load. I then thought it may be the RCD. When I tested the RCD I got >51ma on a ramp test and 1x >40 and 5x >400. I then changed the RCD for a new one and got the same readings. I have tested with all loads disconnected and still the same.


Answers on a postcard
 
Ze of 0.01!
Blimey you could have some massive PSSC. Probably nothing to do with your problem but that is an extremely low Ze. What's the breaking capacity of the mcbs etc?

Tell me about it, its like 24.1 kA, if to go by mesured 241V, your gear would not handle that, its like 4 times braking capacity of your standard 6 kA mcb, I think you ment Ze=0.10 ohm ....
 
Last edited:
Reading through this thread I noticed there was an issue if the socket on the cooker plate was used under load....Have you considered checking the cooker switch, cooker connection and the actual cooker itself, these things are bad at causing RCD issues..
 

Reply to Help needed with an RCD question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
690
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top