Help needed with codes. Pictures included | on ElectriciansForums

Discuss Help needed with codes. Pictures included in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

smiffey

Hi All
Carried out an inspection on Friday and just fill out the forms and i need some help.
1st- what code do i have to give non shower rated downlights in a bathroom? i think it should be= C1
2nd-what code for for no end to end insulation resistance on the house ring? =C2
3rd-what code for an insulation resistance of 2.59 M ohms on the downstairs lights =C3
4th- the picture below is in zone 2 so i think its as high a code as can go as its 0.6m of zone 1 = C1
View attachment 12133 View attachment 12134

C1 = DANGER PRESENT RISK OF INJURY IMMEDIATE REMEDIAL ACTION REQUIRED
C2 = POTENTIALLY DANGEROUS URGENT REMEDIAL ACTION REQUIRED
C3 = IMPROVEMENT RECOMMENDED

Thank you advance for any help or advice.
Cheers
 
Hi All
Carried out an inspection on Friday and just fill out the forms and i need some help.
1st- what code do i have to give non shower rated downlights in a bathroom? i think it should be= C1 -- If the lights are above 2.25m then they're outside zones and no requirement for "shower rated lights"
2nd-what code for for no end to end insulation resistance on the house ring? = C2 -- What is end to end insulation resistance. Do you mean end to end continuity?
3rd-what code for an insulation resistance of 2.59 M ohms on the downstairs lights =C3 -- Although 2.59MΩ is quite low, anything over 2MΩ is OK
4th- the picture below is in zone 2 so i think its as high a code as can go as its 0.6m of zone 1 = C1 -- Pictures not working
View attachment 12133 View attachment 12134

C1 = DANGER PRESENT RISK OF INJURY IMMEDIATE REMEDIAL ACTION REQUIRED
C2 = POTENTIALLY DANGEROUS URGENT REMEDIAL ACTION REQUIRED
C3 = IMPROVEMENT RECOMMENDED

Thank you advance for any help or advice.
Cheers

​My red
 
Cheers for the replys, first off tge lights are at 2.30m so 5mm over! I thought with it being so close id flat it as c1.
2nd off sorry for the typo i was ment to say contunity. I was reading on gn3 and wrote what i was reading by mistake. The result was comeing back 0.00
3rd i understand that anything under 1 is a fail anything under 2 requires futher looking at but what about something so close to 2M ohms
4th i will have to fire the pc up in the morning and repost the pics as im now on my iphone.

Hope that clears a few things up
Cheers
 
Hi All
Carried out an inspection on Friday and just fill out the forms and i need some help.
1st- what code do i have to give non shower rated downlights in a bathroom? i think it should be= C1 Without knowing the type of fitment and location of the lights with regards to shower etc can't really say. At a guess C3, are the lights suitable for the environment? Are they directly above the shower and at risk of splashes and moisture etc? Is there good ventilation?
2nd-what code for for no end to end insulation resistance on the house ring? =C2 Do you mean continuity? If so C2, as the cables will more than likely be working above their CCC. Possibly even a C1.
3rd-what code for an insulation resistance of 2.59 M ohms on the downstairs lights =C3 Still within acceptable limits but what is the age and nature of the installation? I wouldn't code it however I would state that although the figures are within acceptable parameters I would expect the readings to be higher and recommend further investigation.
4th- the picture below is in zone 2 so i think its as high a code as can go as its 0.6m of zone 1 = C1 Piccy no worky...


C1 = DANGER PRESENT RISK OF INJURY IMMEDIATE REMEDIAL ACTION REQUIRED
C2 = POTENTIALLY DANGEROUS URGENT REMEDIAL ACTION REQUIRED
C3 = IMPROVEMENT RECOMMENDED

Thank you advance for any help or advice.
Cheers
My twopenneth for what it's worth...

Without knowing the age and use of the installation these are very rough guesses. What edition was it installed to?
 
Seen as you posted just as I was trying to think, it takes me a while:

RFC continuity coming back as 0.00 ohms? Did your MFT show open or closed circuit? If it shows closed circuit then all is good with very little resistance on the cables although I would annotate it as 0.01 ohms on the sheet.
 
I wouldn't call the lights being close a C1. At the end of the day they're outside the zones and there's no requirements in the regs for IP rated lights. If you're that concerned, give it a C3 (Improvement Recommended)

Are you saying the end to end on the ring is open circuit? Is it on all 3 conductors? If so then there's a break in the ring somewhere. C2 IMO.

I would pass the IR (2.59MΩ) but would recommend that the installation is inspected at shorter intervals.
 
RFC continuity coming back as 0.00 ohms? Did your MFT show open or closed circuit? If it shows closed circuit then all is good with very little resistance on the cables although I would annotate it as 0.01 ohms on the sheet.

That would be a very short ring circuit
 
check the CPCs arent twisted together in the board for end to end of the cpc

was it end to end of line, neutral or cpc you got 0.00ohms which is a closed circuit and would be a very short bit of cable or a very large CSA of conductor to get a reading like that

I tested a newly installed CCU other week and the lad who had installed it had twisted all cpcs in the sockets and at the board but hidden at back then 2 seperate bits of sleeve on the ends looked as if they were seperate until i moved some of the cables out the way and all became clear
this was after i had checked that i had identified correct legs of ring and checked all socket outlets
 
To get a reading of 0.01Ω on a 2.5mm² would suggest that it was only 1.35m long (0.01 ÷ (7.41 ÷ 1000) = 1.35m)

Were all the sockets next to the CU???
 
All the answers are in the Electrical Safety Councils guide, equipment in zones, ineffective earth, discontinues conductor etc.
 
check the CPCs arent twisted together in the board for end to end of the cpc

was it end to end of line, neutral or cpc you got 0.00ohms which is a closed circuit and would be a very short bit of cable or a very large CSA of conductor to get a reading like that

I tested a newly installed CCU other week and the lad who had installed it had twisted all cpcs in the sockets and at the board but hidden at back then 2 seperate bits of sleeve on the ends looked as if they were seperate until i moved some of the cables out the way and all became clear
this was after i had checked that i had identified correct legs of ring and checked all socket outlets

I was on a job the other week n another contractors apprentice was askin bits n bobs about testing even he said this was his pet hate Only come across it twice where twisted outside DB n seperated inside God there are some absolute numptys out there
 
Hi all,
Strima, The bathroom lights are normal mains gu10 lamps and arnt directly over the shower but could defenatly have contact with stram and moisture.

Strima & jud, brucelee, mogga the end to end was belling out ok as that was one of the first things i checked with my fluke t5's it was belling on line to line, eathr to earth and neutral to neutral i also belled out every wire against every wire to check for cross connections and it all was fine. Then when i put my actull testers fluke mft 1653 on i got a result of 0.00 on all the wires. The circuit is the hole house ring 13 sockets in total, not insludeing the kitchen ring on a diffrent mcb. also the earth was two seprate wires and i pulled a bit of the slack down and checked and re sleved.

The house was wired to the 16th edition at a gess as there was a huge rccd device in line on the main tails. The wires were solid copper but black and red in colour and by how low the insulation resistance is id say comeing very close to the end of its life so 20 - 25 years?
 
Last edited by a moderator:

Reply to Help needed with codes. Pictures included in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top