Just been to look at a hob that has been getting hot above the electrical / gas connections. I was unfortunately unable to locate the source of the problem.

No visible damage to cables,
Zs fine,
RCD checked out fine,
IR >999 @500v,
And is still fully operational.

I’m Baffled, any ideas?

[ElectriciansForums.net] Help needed with hob fault


[ElectriciansForums.net] Help needed with hob fault


[ElectriciansForums.net] Help needed with hob fault
 
There is no isolation for the gas other than the main isolation valve at the meter.

The Hob is being replaced by another person arranged with the landlord - I can only ensure that there is no immediate danger from the electrical side.
 
https://s3-eu-west-1.amazonaws.com/howdens-howden-prod/web_content/media/library/pdf/3168.pdf

On page 19 of this link one can see the mains connection for this hob. Is this directly underneath the hot spot you photographed?

If this is an electrical problem I wonder if the earth connection terminal for the hob is welded directly to the metalwork underneath the hotspot. If so, then perhaps a high current has flowed through this weld and terminal down the flex to the plug and thence to the RFC cpc back to the MET. If the current was high enough (and its square) and conductivity of the welded connection low significant Ohmic heating may have taken place.

For the location of the origin of such an earth fault current I would:

a. check the presence and conductivity of gas and water bonds back to the MET.

b. check the earthing and IR of electric showers, immersion heaters central heating system (which may have their metal water pipes connected to the gas pipes through the HW and CH system). It could be they have L-E or N-E faults which are being routed partly or in full through the gas pipe to the hob and then to its mains supply cpc.

c. the earthing system and it correctness ie: MET, earthing conductor, means of earth, TT, TNCS, TNS...

Just some musings for you to consider - you get the sense of what I mean.
 
How many cans have you had /you sure its tobacco in those smokes?
don't do cans. they usually contain that fake beer called lager. one reason them germans lost 2 world wars. they hadn't got real ale to sustain them.
 

Reply to Help needed with hob fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
994
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top