New Wylex dual RCD board

RCD 1 (80A 30mA)

32A Cooker
32A Kitchen ring
6A Upstairs lights

Have tried disconnecting all loads and connecting one at a time to see if I can determine which circuit is causing the problem but take your pick - whichever one I connect up trips the RCD.

RCD 2 (63A 30mA) with ring and downstairs light is all working fine.
 
When you say disconnecting, do you mean neutrals as well?

What hapens if RCD2 is switched off when you try connecting any circuit?

How is the 2-way lighting wired?

Simon.
 
Didn't do any testing prior to disconnecting old CCU. I'm doing it in my house and we've not had any issues prior to now.

Yes, have also tried disconnecting neutrals. Doesn't matter if RCD 2 is switched on or off.

It might be fooked!

No, no neutral in the wrong bar.
 
sounds like you have neutral to earth fault you need to do insulation resistance test between l+n and l+e and N+E before connecting them in one at a time....
 
Didn't do any testing prior to disconnecting old CCU. I'm doing it in my house and we've not had any issues prior to now.

Yes, have also tried disconnecting neutrals. Doesn't matter if RCD 2 is switched on or off.

It might be fooked!

No, no neutral in the wrong bar.

That could be a costly mistake as testing before a CCU change is perhaps the most important part of it.

So if all neutrals are in the right bar then it's a borrowed neutral, a reversed polarity, poor insulation resistance or a fooked RCD. the fooked RCD is quite simple swop them over and put the non tripping one in and see if it holds.

If it's nay of the others then testing would be the next step.
 
Seriously, check the RCD before you go dismantling any circuits. It's not unheard of for wylex RCD's to be faulty out of the box.
 
swap the rcd's, ie use the one that is ok and put it over to the side that is tripping! if this trips, then its not rcd, or ramp test both rcd's on the side that is working to see if both are ok?
 
first thing i would do, swop the lights so they are on the same RCD. if that cures the problem, you have a borrowed neutrasl on the lights. most likely the 2 way landing light. either leave light circuits both on same RCD or rewire the offending circuit. all else fails, call in the A team.
 
Thankfully resolved. Fooked RCD. Most frustrating but you live and learn. Grateful to all for your sugestions - useful for the next time something similar happens.
 

Reply to HELP! New CCU, RCD keeps tripping??? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
188
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
580
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
538

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
478
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
655
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top