I have a practical exam on Thursday and have just found out I have to perform a test that I haven't yet covered(my own bloody fault)
So at this late hour I am getting a bit concerned.
I have a length of SWA 2.5mm 3 core wired into a CU at one end and an isolator at the other.
Could someone please explain simply to me how to perform 1,Continuity 2,Ins Resistance and 3,Polarity on the SWA
I have some idea but with a million thigs running through my head I need some help.

Thanks in advance

Gerry
 
Isolate cu

1)remove conductors from cu terminals
2) connect line to cpc of swa & test continuity at the load side of isolator between line & cpc, turn isolator on/off while testing prooves line is switched (R1+R2 done & polarity)
3) remove link between line & cpc
4) set meter to 500v test IR between line & cpc
5) test IR between neutral & cpc
6) test IR between neutral & cpc
 
Isolate cu

1)remove conductors from cu terminals
2) connect line to cpc of swa & test continuity at the load side of isolator between line & cpc, turn isolator on/off while testing prooves line is switched (R1+R2 done & polarity)
3) remove link between line & cpc
4) set meter to 500v test IR between line & cpc
5) test IR between neutral & cpc
6) test IR between neutral & cpc


Thanks very much,very helpful

I see that steps 5 and 6 are the same,should step 5 be test IR between line and neutral.

Either way thanks again!
 

Reply to Help Please! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
778
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
Hi all, I am doing level 3 design project assignment where I have to calculate the lights for the pool. Area of the pool is 148m2. Light...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top