Hi guys, I would very much appreciate some advice here!! Basically was called to a school, every time they clicked the light switch, the RCD in the CU tripped. Meggered the circuit L to E over 299 ohms, E to N, over 299 ohms, but L to N 0.01 ohms. This is correct on a lighting circuit with fluorescent fittings. R1, R2 values all good. This leads me to the conclusion that one of the flo. fittings has become faulty (possibly a small amount of current leaking through to the cpc inside the fitting? But if that was the case, wouldnt that show up on the megger test? When i disconnected the cpc from the CU on that circuit, the lights stayed on! How is the best way to discover the faulty fitting? A lot of head scratching going on today!!!! Any help greatly appreciated, thank you guys.
 
reason i asked the number is that there may not be a fault as such. florries are notorious for having a bit of leakage. 8 lights can be OK but add 2 more and the cumulative might just push the RCD over it's threshold, esp. if it's a bit sensiitve, like about 22mA.
 

Reply to Help please!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
831
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top