Just been looking at a condition report from a property a friend is buying.
Its a TT system, Ze measured at 200 Ohms earth rod.
Ring final circuit 2.5mm, 30mA RCD, the measured Zs is 9.8 (max allowed is 1.44)
There is a 100ma main switch with operating time of 327ms.
The report says Satisfactory, is this the case???
Thanks
Its a TT system, Ze measured at 200 Ohms earth rod.
Ring final circuit 2.5mm, 30mA RCD, the measured Zs is 9.8 (max allowed is 1.44)
There is a 100ma main switch with operating time of 327ms.
The report says Satisfactory, is this the case???