Hi all, I'm working on some maintained
em lights at the moment and theyrr doing my head on grr! They work fine as ems on power failure. but won't strike when power is restored. then, randomly one or two will come back on over 24hourd or so . they're tridonic combi ballasts on single 49w tubes. I've swapped some for new ballasts but the problem persists. Any ideas?
 
As Tazz has said it has to be on the control side,if the fittings are new then that rules out a problem with fittings as its unlikely they are all faulty,try testing for a voltage with something that puts a load on the circuit rather than a digital meter as the current drawn by a meter is very small and sometimes they will read say 240 v but when you put a load on the voltage disappears and it can be someting as simple as a loose connection but relying on the meter saying you have the correct voltage there you spend ages chasing your tail.
 
Had a similar problem months ago with tridonic combo ballasts. Lamps would strike and stay lit on battery back-up, restore the mains and lamps would flash twice and stay off. Turned out to be faulty lamps.

Try new lamps as nick suggested in post #10 if you haven't already.

Keep us posted if you get to the bottom of it.
 
Well gentlemen, the problem has gone away for now but without me finding the solution...

In response to the voltage questions, the fittings that are faulting are on a circuit of 10 lights and only 2 or 3 are faulting - voltage is ok.

The batteries in some of the fittings are brand new - the original fault developed when I was changing the packs after they failed the 3 hour discharge test and I'd had the circuits turned off. As described above by Merl, they flashed twice on restart then wouldn't come back on.

When I got there yesterday most of them had come back to life.

Tried changing the lamps in the remainder to no avail and finally changed the ballasts again and the tinkers worked.

I've returned the ballasts to the supplier and asked to be informed if anythings found...
 

Reply to Help wanted with em fittings please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

You really need an inductance or LCR meter or a ring tester which are expensive to buy but you can make your own ring tester if you want a project...
Replies
1
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top