Help wiring a ceiling rose

In the room there is two holes in the ceiling

Below is a picture of the first hole
It only has two wires
The second hole has one wire

I think I am missing a wire for the switch?
Is it possible that this old house only has 2 wires?

When I turn on the electric, the light doesn't turn on
There is current in the wires because I have a device to check
Do I have to cut more holes to check for another wire?
Thanks

rose.jpg


plan.png
 
@westward10
Here's the wiring at the switch
I'll connect the earths now, I'll need to strip, would not connecting the earths stop the light from turning on?

@gaz_sparky
Looks like I'll have to cut more holes for that missing a cable
Here's the other hole with one wire, I not sure if this is correct
Does 3 plated wiring only have 2 wires?

@SJD
I think the second hole is the last light in the circuit
Due to its location and it only had one wire
The switch wire only goes to the first light in the circuit?
It doesn't trip


The text on the switch is
COMMON
6AX250V
AC ONLY
1 WAY 2 WAY

Thanks

rose2.jpg


switch.jpg
 
This is speculative but shouldn't cause a problem. Put the browns at both roses together at the terminal the brown from the flex is connected at. If this fails you need the services of an electrician as there has obviously been some modifications taken place. ISOLATE THE POWER FIRST.
 
Judging by the red singles in the switch this installation is very old. I suspect Diazed fuses are probably still in service, and the Earthing and bonding as well as meter tails are likely to be inadequate. The main protective conductor (neutralising link) may well also be undersized.

I would strongly recommend that a Registered Electrical Contractor be contacted and a Periodic Inspection Report be commissioned.
 
As Westward10 & Risteard said ^^^
Personally I would suspect that the switch wires goes into a junction box somewhere and the lights are fed from there, in which case the brown conductors should be looped together in the same terminal with the brown flex at the first ceiling rose, then the single brown and the the brown flex together in the same terminal at the last rose.
But my advice is to get in a spark to check it out as there are no cpc's connected which could/will be a problem especially if you have any metal fittings anywhere on this circuit. There could also be other defects which you may not be aware of that might affect the safety of this install.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
bman_89,
Last reply from
Risteard,
Replies
27
Views
2,980

Advert

Back
Top