I'm not sure about this - could somebody confirm my thoughts here:

The old Honeywell thermostat needed a neutral as it has a small heater resistor to reduce the hysteresis of the bimetallic strip. Photo below of the connections. From that the grn/yel wire appears to be permanent live in, the brown wire switched live to the boiler, and blue neutral.

But the new Honeywell Home thermostat, from the OP's picture, is battery powered and acts effectively as just a switch, and doesn't require a neutral.

So I think the green/yellow should go to terminal A, and the brown to terminal B, and the neutral safely terminated and not connected to the new thermostat at all.

Karatekid - does the lid of your old thermostat have the same diagram in it as the pic below, or any other info about which terminal is which? I do believe what you have called the 'earth' wire is very likely to be mains live, so I don't recommend experimenting until we are more certain of exactly which wire is which.

Anyone?
[ElectriciansForums.net] Help wiring Honeywell DT2 thermostat
PS If the above is correct, and you leave the wires as you first connected them, but put the grn/yel into C, I think the boiler will run when the thermostat is off, and go off when the thermostat is on!
It works!!!! Green/yellow into A and Brown into B with Blue blocked off thank you!!!
 

Reply to Help wiring Honeywell DT2 thermostat in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
Replies
8
Views
532
The 4 pumps are :- 1. boiler to cylinder 2. C/H and UFH circulating pump 3. UFH dedicated pump after manifold 4. DHW circulating pump. (this just...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top