that sounds good are the readings im getting 148v right then.
could you point me in the right direction on how to change star to delta im fairly new to motors
also do you know if i can use this inverter just as a phase changer and not have to set the freq
thanks
 
your meter is reading 148v because the circuitry of your meter is calibrated to read voltage at 50Hz, your inverter is not putting out voltage at 50Hz so you are getting weird readings. in the motor terminal box you should find your star point, jumper bars connecting u2,v2,w2 together, remove these and connect to opposite terminals, u1/w2, v1/u2, w1/v2, your now delta connected, let me know how you get on:)
 
Last edited by a moderator:
Some questions -

  • You say you are putting in single phase ? exactly what - Single phase 230V or dual phase 400V.
  • Is the unit a single/3 phase, single phase only or 3 phase only. Which of the possible input voltage ranges is it ?
  • What is the model number of the invertor you are using ?
  • The manual provided and the model number to give you out exactly what input / output volts and frequency you need and should have.
0.75 kW = 1hp, so your motor is 2.5 HP.

Sorry to ask so many questions, but the information supplied is not enough to do anything other than take a wild guess to fill in the blanks and try to give an answer. Also unless we know the full information then acting on any response could potentially cause damage to both the equipment and more worryingly yourself or others.
 
right i have a 380-420vy 1.85kw motor not sure on hp
inverter is a ac tech scf series
wired the single phase in and 3 phase out but does not work
volt meter reads 148v at each phase to ground but phase to phase 0v have i set it up wrong can anyone help
heres the manual thanks
http://www.ctiautomation.net/PDF/AC-Tech/AC-Tech-SCF-Drives-Installation-Operation-Manual.pdf

At no point in the op does it list the particular model number in question. The linked manual lists 32 different model types, of varying parameters. Until such time as we know exactly which model we are dealing with then this entire thread is full of nothing more than educated guesses. Guesses can be both dangerous and deadly.
 
bomjac, i apologise and stand corrected, but this aint rocket science, if i was asking these questions i would be sacked on the spot, but the op hasnt much motor experience so maybe i'm being complacent, 32 different types? of models ? yes, of input and outputs?? dont think so. ill hand this over to you m8, later.
 
Some questions -

  • You say you are putting in single phase ? exactly what - Single phase 230V or dual phase 400V.
  • Is the unit a single/3 phase, single phase only or 3 phase only. Which of the possible input voltage ranges is it ?
  • What is the model number of the invertor you are using ?
  • The manual provided and the model number to give you out exactly what input / output volts and frequency you need and should have.
0.75 kW = 1hp, so your motor is 2.5 HP.

Sorry to ask so many questions, but the information supplied is not enough to do anything other than take a wild guess to fill in the blanks and try to give an answer. Also unless we know the full information then acting on any response could potentially cause damage to both the equipment and more worryingly yourself or others.

surely some of your questions are answred in the op. you ask single phase or dual phase. he says single phase, and 3 phase out. maybe I can't read???. as usual there is someone who asks over the top questions rather than help.
 
If its a single phase input inverter (ie. 230vac) then you will not get 380-420v to your motor!!!

If you have a dual voltage motor, where you can use 3ph 230v D... you may be in luck.


.
 
At no point in the op does it list the particular model number in question. The linked manual lists 32 different model types, of varying parameters. Until such time as we know exactly which model we are dealing with then this entire thread is full of nothing more than educated guesses. Guesses can be both dangerous and deadly.

I'll hazard a guess at SF230Y

.
 
Just going on past experience have you got a pot or resistor connected to the speed reference? No resistance = no speed. Also where is the safety contactor fitted? If after the VFD it needs to be closed before the VFD is energised.
 
hi thanks for all you replies
all i want to do is make my 240v supply work my 3 phase motor as i think this inverter will do this job
i will get the full part number today of the scf
the motor has 2 voltage ops on it one is 380-420v Y
the other being 220-240v delta 2820 r/min 3-50hz
i asume this is what you mean if your asking if the motor is dual power thanks

thanks for all you help everyone i will let you know how it all goes tonight
 
Hi,
as you have said the motor is a dual voltage type, first, the motor needs to be wired for 220-240v delta. then you need to access the inverter program parameters to set the current limit and overload levels for the motor, this would protect the motor if any thing went a miss.
you will have to decide which stop start set up you need for your application, i personally would use two wire stop start using preset speeds,fwd and rev. i would use an accel time for starting(soft start) and coast to stop.
the strange voltage you are getting are down to the fact that the out put voltage of the inverter is DC pulsed to simulate AC.
 
hi guys i have wired the motor to each opposite terminal which being v2-w1 u2-v1
u1-w2 is this right or have i got to wire it to the terminals you said
also the inverter came in a prefab box which has on off sw and a dial for freq (but this is broken) and a reverse sw
at the moment all it is doing is buzzing wont spin thanks
 
See my last post, I asked if there was a pot on the speed reference. It’s usually 0 to 10K linier. I normally use a 10 turn wire wound. Read the rest of the post as well!
Motor connections
Delta
U1 > V2
V1 > W2
W1 > U2
Star
U1
V1
W1
U2,V2 & W2 bridged
 
Motor to be connected as:

[ElectriciansForums.net] help wiring inverter to car ramp


You'll need to drill through the parameters ensuring motor base speed is 50Hz, motor voltage is correct, control is via terminal strip and speed is via potentiometer. Is this motor fitted to the ramp (ie. under load) or is it buzzing on the bench (ie. not under load)?

We're assuming your motor is new or is known to be in a fully operational condition or tested for electrical balance.

The manual is pretty decent and will be your biggest help. Any model number yet?

.
 
Last edited by a moderator:
The manufactures usually offset the connections so you can fit links in a straight line to the opposite terminal.

Top row
U1 V1 W1
Bottom row
W2 U2 V2
 
model is sf250yf-787
so i just wire strait across as pic shows

got it moving now it was down to the broken sw i just need to run it at 50 hz i assum
thanks for the help every one cheers
 

Reply to help wiring inverter to car ramp in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Of course it would, but I'd have needed a motor with the correct flange and shaft to fit the pump. My ramp cost me a total of £100 + the new coil...
Replies
6
Views
3K
Baja wiring harness LED light help. I've fitted a US Baja harness on my Australian FJ, but I need to replace the Baja harness switch setup so...
Replies
0
Views
961
Good day I have the same fault coming up on an inverter but different circumstance. Customer for some reason enabled Amorphous mode while not...
Replies
5
Views
5K
T
  • Question
Kirrchoff's law for series circuits states that the sum of the volt drops across the series loads will be the same as the generated voltage. The...
Replies
16
Views
9K
If I was to use a lift for mainly 4x4s I would’ve going for something bigger than 2500kg. OK if you have a couple of Suzuki Jimnys but a Discovery...
Replies
10
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks