Can you not disconnect feed to motor at the s/d contactor? Yes, 500V only to begin with and perhaps let us have a look at the readings. The continuity should all be about the same. IR depends on the state of the windings.
 
The size of that motor unless something about it's frame size, shaft size etc is really uncommon. If it has been a winding failure, it'll be more cost effective to buy new rather than re wind.

I've always found the break even point to be around 30kw and bigger is worth rewinding.
 
Don't substitute... diagnose! Changing the contactor might fix it, but only in the same way that fitting a new engine might fix a car that won't start.

You should be able to verify the motor condition with 90% certainty using about ten 5-second tests, done from the control cubicle if it's more convenient than at the motor. Test the windings from the motor side of M and D; obviously you wouldn't be able to distinguish between a winding fault and a damaged cable - but at least you will be able to identify a disconnect, an interwinding short, a single winding short etc. IR from each winding to each other and to earth at 500V, and resistance of the three windings each of which will have one end on M and one on D (&S).

If something is amiss - insulation down, one winding O/C, or more than say 10% difference in winding resistance - then you will have to repeat the tests at the motor terminal box. The operation of the contactors can be proven likewise at either end, provided you can keep the control supply on with the 3-phase off. Or if live testing is permissible then you can probably find the fault with just the three line current clamp tests in a matter of seconds.
 
Been reading this thread and making me even more twitchy than when I started.
Got a star delta starter sat in my van for over 2 months now. Been putting job off as it's for a 40 year old compressor or may be older with the old style starters where you flip a lever down to start it then quickly up to run but it won't stay up any more. ( waiting for the puns )
Plus the building is a old aircraft hanger that was removed from local raf base some time after the war and rebuilt on site and I don't think the electrics have been touched since. Need to discuss with customer all the work on mains that need doing first.
 

Reply to Help with 3 phase star delta motor in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
  • Question
Here are the other drawings
    • Optimistic
    • Funny
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top