I have a 110 5kva transformer. Run it off a 30 meter exstension lead running from the house into the Work shop. The transformer works and powers all machines
I've now installed a 6 mm armoured cable running length 30 meters on a 32amp breaker to the woek shop. When plug the transformer into the work shop sockets it trips the breaker. But socckets runs every thing else with out tripping. What could be the problem ?
 
Have you tested the ZS at the end of the SWA? Only thing I can think of personally is when it's initially powered up there's a slight surge but does sound a little odd.
 
Just tried a extension lead in the work shop. Now that powers the transformer Fine. Just a direct plug to sockets to the sockets trips. Just cant think why
The added resistance of the extension lead (probably 1.5mm at most) is much more than the 6mm SWA, so any surge from the transformer now lacks that extra mitigation.

As @westward10 says you need to tell us more about the type of MCB, etc. Often for transformers a D-curve is used to avoid such trips, but that also has issues of achieving low enough Zs to meet disconnection times.

For a 5kVA transformer at 230V Hager recommend wither 63A C-curve or 32A D-curve. A 32A BS88 fuse has easier-to-meet Zs for similar surge capacity, but not nearly as convenient as a MCB.
 
For a 5kVA transformer at 230V Hager recommend wither 63A C-curve or 32A D-curve. A 32A BS88 fuse has easier-to-meet Zs for similar surge capacity, but not nearly as convenient as a MCB.
I would add that those MCB recommendations are for fault protection, not for overload protection of the transformer. It might have its own protection on the primary (230V) or on the secondary (110V) sides, but check the manufacturer's recommendation for supply protection first.
 

Reply to Help with a transformer in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
750
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
629
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top