Hi Guys,
I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used.
The fuse board is an MEM Memera 2000
the downstairs ring is on a 32A 60898 MCB, protected by a 61008 RCD 100A 30mA
there are 2 other circuits on the same RCD which are the upstairs rings on a 32A 60898, and the shower also on a 32A 60898

The customer had this problem before I came and had already tried replacing the washing machine and getting the same problem.
  • we have carried out fault finding and also EICR'd the whole house with perfect results,
  • we have tried plugging in the washing machine upstairs which is the same RCD and it didn't trip. and also on another circuit in the garage on a different RCD which also didn't trip (both times the washing machine stayed in the same position in the kitchen under the worktop and was just plugged into different sockets via an extension lead
  • we have also tightened all connections on the downstairs ring assuming that maybe the washing machine vibrating could have caused a loose connection and tried fault finding again and cant find any problems
  • we have also tested for overload by unplugging every other thing on the circuit and it still trips
  • we have also replaced both the RCD and the MCB and still it keeps tripping
  • I have tried plugging into other sockets on the same circuit and it still trips
  • I have also tried replacing the socket its plugged into just in case

Yet we cant find any fault so I'm absolutely stumped, is there anything I've forgotten to do?

Thank you in advance, I'm loosing hair over this problem haha

Test results for Downstairs socket ring
R1 0.57
RN 0.57
R2 0.95
R1+R2 0.38
Zs 0.63
RCD 1/2x didn't trip
RCD 1x 27.8ms
 
OP stated that machine was tested on another circuit covered by the same RCD and didn't trip. Not conclusive, but suggests that cumulative earth leakage may not be the issue.
He still needs to know what the accumulative earth leakage is.
 
He said it works fine on another circuit, which means that the circuit its on now could have higher accumulative earth leakage than the other circuit.

Actual statements from opening post below:

  • we have tried plugging in the washing machine upstairs which is the same RCD and it didn't trip. and also on another circuit in the garage on a different RCD which also didn't trip (both times the washing machine stayed in the same position in the kitchen under the worktop and was just plugged into different sockets via an extension lead
  • we have also tested for overload by unplugging every other thing on the circuit and it still trips
  • I have tried plugging into other sockets on the same circuit and it still trips

The last point would also seem to rule out my (already unlikely) suggestion that isolator could be problematic.
 
Actual statements from opening post below:



The last point would also seem to rule out my (already unlikely) suggestion that isolator could be problematic.

Although IR tested, it still doesn't rule out that earth leakage could happen when a load is put on that circuit.
Therefore, an earth leakage test would be the next step.
 
Although IR tested, it still doesn't rule out that earth leakage could happen when a load is put on that circuit.
Therefore, an earth leakage test would be the next step.

It would be a sensible step to rule out the possibility, although tripping seems to be limited to this one circuit and tripping continues with all other loads disconnected. As such cumulative leakage doesn't appear to be the issue if this machine trips when no other loads are present and leakage from machine itself appears to be no issue when connected to other circuits. That this applies on circuits protected by same RCD would suggest overly sensitive RCD is also unlikely to be the problem.

Whatever the issue, OP's efforts would seem to suggest that it stems from the circuit to which the appliance is normally connected.
 
It would be a sensible step to rule out the possibility, although tripping seems to be limited to this one circuit and tripping continues with all other loads disconnected. As such cumulative leakage doesn't appear to be the issue if this machine trips when no other loads are present and leakage from machine itself appears to be no issue when connected to other circuits. That this applies on circuits protected by same RCD would suggest overly sensitive RCD is also unlikely to be the problem.

Whatever the issue, OP's efforts would seem to suggest that it stems from the circuit to which the appliance is normally connected.

I'm wondering if the OP did an N + L 250v IR test ? That would give an indication that all loads are indeed disconnected.
 
Hi Guys,
I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used.
The fuse board is an MEM Memera 2000
the downstairs ring is on a 32A 60898 MCB, protected by a 61008 RCD 100A 30mA
there are 2 other circuits on the same RCD which are the upstairs rings on a 32A 60898, and the shower also on a 32A 60898

The customer had this problem before I came and had already tried replacing the washing machine and getting the same problem.
  • we have carried out fault finding and also EICR'd the whole house with perfect results,
  • we have tried plugging in the washing machine upstairs which is the same RCD and it didn't trip. and also on another circuit in the garage on a different RCD which also didn't trip (both times the washing machine stayed in the same position in the kitchen under the worktop and was just plugged into different sockets via an extension lead
  • we have also tightened all connections on the downstairs ring assuming that maybe the washing machine vibrating could have caused a loose connection and tried fault finding again and cant find any problems
  • we have also tested for overload by unplugging every other thing on the circuit and it still trips
  • we have also replaced both the RCD and the MCB and still it keeps tripping
  • I have tried plugging into other sockets on the same circuit and it still trips
  • I have also tried replacing the socket its plugged into just in case

Yet we cant find any fault so I'm absolutely stumped, is there anything I've forgotten to do?

Thank you in advance, I'm loosing hair over this problem haha

Test results for Downstairs socket ring
R1 0.57
RN 0.57
R2 0.95
R1+R2 0.38
Zs 0.63
RCD 1/2x didn't trip
RCD 1x 27.8ms
UPDATE
so I changed the faceplates and still it kept tripping,

Now I've switched the downstairs sockets with the 32A cooker circuit on a different RCD and now everything seems to be running smoothly,
So does this mean it is accumulative earth leakage across all 3 of the circuits (down sockets, up sockets & shower) on the tripping RCD that must have been causing my problem?
As the RCD is exactly the same as the one that was originally tripping

Cheers for all your help everyone!
 
UPDATE
so I changed the faceplates and still it kept tripping,

Now I've switched the downstairs sockets with the 32A cooker circuit on a different RCD and now everything seems to be running smoothly,
So does this mean it is accumulative earth leakage across all 3 of the circuits (down sockets, up sockets & shower) on the tripping RCD that must have been causing my problem?
As the RCD is exactly the same as the one that was originally tripping

Cheers for all your help everyone!

The isolator was always going to be an unlikely option and previous information seemed to have ruled out the possibility. If I can remember correctly the issue is limited to this one circuit and you had tried disconnecting all other loads on the circuit , which effectively rules out any cumulative effect (unless some load was overlooked).

I can't remember all previous information, but believe the washing machine had already been replaced. The post above is where you need to be, with ramp testing of RCD and determining leakage from appliance, circuit to which it is connected and all circuits connected to this particular RCD, although it didn't trip when machine was connected to another circuit protected by the same device.
 

Reply to Help with a tripping washing machine in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Assuming you are a novice to electrics? As in no access to electrical equipment. Plug something in to the sockets that you know works else where...
Replies
1
Views
381
Cbelectrics
C
You may still have a problem with earth leakage though, it could be that the Samsung has less leakage than the Bosch ones. If you do get a random...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top