Just been at Church hall with 3p TT supply, My query is we carried out a PIR on it,it has no 100ma rcd protection of church metal consumer units mentioned on cert but we are only certifiying church hall.
Church hall has 100ma 4 pole rcd up front onto metal switchfuse 3036 60A protection on to 16mm4c swa with separate earth to metal consumer unit fitted with an other 100ma rcd in it and rcbos on some circuits.
My problem is on testing the 100ma in the church is quicker than the one in church hall therefore need a 100ma 4 pole time delay rcd but cannot seem to find any stockists of these. Would it be acceptable to fit a 300ma upfront to protect complete installation even this this mainly for fire protection?
Thanks
Church hall has 100ma 4 pole rcd up front onto metal switchfuse 3036 60A protection on to 16mm4c swa with separate earth to metal consumer unit fitted with an other 100ma rcd in it and rcbos on some circuits.
My problem is on testing the 100ma in the church is quicker than the one in church hall therefore need a 100ma 4 pole time delay rcd but cannot seem to find any stockists of these. Would it be acceptable to fit a 300ma upfront to protect complete installation even this this mainly for fire protection?