M

mainebankelec

Just been at Church hall with 3p TT supply, My query is we carried out a PIR on it,it has no 100ma rcd protection of church metal consumer units mentioned on cert but we are only certifiying church hall.

Church hall has 100ma 4 pole rcd up front onto metal switchfuse 3036 60A protection on to 16mm4c swa with separate earth to metal consumer unit fitted with an other 100ma rcd in it and rcbos on some circuits.

My problem is on testing the 100ma in the church is quicker than the one in church hall therefore need a 100ma 4 pole time delay rcd but cannot seem to find any stockists of these. Would it be acceptable to fit a 300ma upfront to protect complete installation even this this mainly for fire protection?

Thanks
 
At present there is no main isolation for the complete building also so to overcome all these problems fit 300ma upfront of everything then to escos to split of for single phase church metalclad consumer units?
 
You should make it time delayed, that's the ONLY way of achieving discrimination with RCD's.
 
There's more than a decent chance that any one of those 100mA RCDs will also take out a non S type 300mA RCD. The only real way of achieving discrimination between RCDs is via A time delay on the upstream RCD!!!
 
There's more than a decent chance that any one of those 100mA RCDs will also take out a non S type 300mA RCD. The only real way of achieving discrimination between RCDs is via A time delay on the upstream RCD!!!

Like in post 9 lol
 
All enclosures of RCDs or consumer units incorporating RCDs in TT installations should have an all-insulated or class 2 construction, or additional precautions, as recommended by the manufacturer, need to be taken to prevent faults to earth on the supply side of the upstream 100mA, S type, RCD.
 
Last edited by a moderator:

Reply to Help with discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
716
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top