All enclosures of RCDs or consumer units incorporating RCDs in TT installations should have an all-insulated or class 2 construction, or additional precautions, as recommended by the manufacturer, need to be taken to prevent faults to earth on the supply side of the upstream 100mA, S type, RCD.
That's why we're suggesting a 'front end' RCD.