Evening..I'm after a bit of advice coding an EICR I have done today, I don't do an abundance of them so just a bit unsure.
1. 3 sockets spurring of a ring without a fused spur.
2. Evidence that ring cables had been joined behind the DB, the L & N end to ends gave me the results I was looking for but the CPC was 0.01 ohms. I tested at a socket with the 2 legs at the board out and got a correct reading which suggests figure of 8 wiring on the CPC.
3. Socket circuit wired through metal conduit buried in the wall with metal back boxes connected, the earths for the sockets have been taken off the back boxes.
4. Back boxes not earthed on various circuits
5. Incorrect colours used on socket circuit.
Thanks in adavnce.