Doomed

-
Arms
Joined
May 26, 2009
Messages
1,132
Reaction score
764
Location
Dorset
Working on report at home, left books in office as I got called home urgently yesterday, help on a couple of codings would be useful. I want to have the report emailed off before Monday so I cant use the NICEIC advice line.

Inspected care home, all clients are dementia.

No RCD protection on majority of sockets in clients rooms, normally this would warrent a C3, but due to the situation would you rate it as C2?

One of the main DB's is in a bedroom with a clients bed directly under it, client often in bed (I had to ask nicely for the staff to move the client so I could move the bed to access the DB). I have no idea if I should code this, if it was storage in the way I would C3 it, but in this situation? I know I would kick off if I was doing a risk assessment, but for an EICR?

May post more later.
 
Working on report at home, left books in office as I got called home urgently yesterday, help on a couple of codings would be useful. I want to have the report emailed off before Monday so I cant use the NICEIC advice line.

Inspected care home, all clients are dementia.

No RCD protection on majority of sockets in clients rooms, normally this would warrent a C3, but due to the situation would you rate it as C2? might lean towards a C2 here if i thought there was a potential danger due to the dementia issue

One of the main DB's is in a bedroom with a clients bed directly under it, client often in bed (I had to ask nicely for the staff to move the client so I could move the bed to access the DB). I have no idea if I should code this, if it was storage in the way I would C3 it, but in this situation? I know I would kick off if I was doing a risk assessment, but for an EICR? no code, but maybe a recommendation on the EICR

May post more later.
my comments in red.
 
Working on report at home, left books in office as I got called home urgently yesterday, help on a couple of codings would be useful. I want to have the report emailed off before Monday so I cant use the NICEIC advice line.

Inspected care home, all clients are dementia.

No RCD protection on majority of sockets in clients rooms, normally this would warrent a C3, but due to the situation would you rate it as C2?

code 3

One of the main DB's is in a bedroom with a clients bed directly under it, client often in bed (I had to ask nicely for the staff to move the client so I could move the bed to access the DB). I have no idea if I should code this, if it was storage in the way I would C3 it, but in this situation? I know I would kick off if I was doing a risk assessment, but for an EICR?

No code, just a comment/recommendation.
May post more later.

.......
 
All portable appliances should be tested at suitable intervals in such an installation, so there is a lower than average risk from the use of portable appliances. So I would only go with a C3 because that's what the guidance in 7671 says it should be for no RCD.

Adequacy of access to switchgear is an item on the inspection schedule, and you can't pass it as it is at the moment as having a patients bed in the way is inadequate access. So that's a C3 as far as I am concerned.
 
Next - am I supposed to be coding for plastic DB's yet? and if so C3?
Also what code is plastic trunking in fire escape routes with no metal clips?
no code at present.
 
Last edited:
Next - am I supposed to be coding for plastic DB's yet? and if so C3?
Also what code is plastic trunking in fire escape routes with no metal clips?

421.1.201 wouldn't apply to a residential care home anyway. The regulation is not intended to apply to consumer units and similar switchgear assemblies in residential care homes or other premises not intended for household use. Regulation 421.1.201 being introduced related specifically to domestic premises, which are not covered by fire safety legislation in the way that premises such as care homes are. The regulation therefore uses the term ‘domestic (household) premises’.
 
421.1.201 wouldn't apply to a residential care home anyway. The regulation is not intended to apply to consumer units and similar switchgear assemblies in residential care homes or other premises not intended for household use. Regulation 421.1.201 being introduced related specifically to domestic premises, which are not covered by fire safety legislation in the way that premises such as care homes are. The regulation therefore uses the term ‘domestic (household) premises’.

I credited the bloke with enough sense to have read the book himself before asking and so assumed the question was a general one rather than specific to this job
 
Sorry, one last quicky, now looking at a EICR from another company on another care home, just want to double check their max Zs values for type C 61009 at 32A and C 60898 at 10A, they have 0.68 and 2.19, can't remember from memory if these are correct, or if they are the revised values or the old ones.
Ta.
edit: also is the min CPC size for a type C still 1.5mm?
 
Last edited:
Sorry, one last quicky, now looking at a EICR from another company on another care home, just want to double check their max Zs values for type C 61009 at 32A and C 60898 at 10A, they have 0.68 and 2.19, can't remember from memory if these are correct, or if they are the revised values or the old ones.
Ta.
edit: also is the min CPC size for a type C still 1.5mm?
take 5% off for cmin and there is an andriod app with the zs values

[ElectriciansForums.net] Help with EICR coding
 
Last edited:

Reply to Help with EICR coding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
719
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
244

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top