Working on report at home, left books in office as I got called home urgently yesterday, help on a couple of codings would be useful. I want to have the report emailed off before Monday so I cant use the NICEIC advice line.

Inspected care home, all clients are dementia.

No RCD protection on majority of sockets in clients rooms, normally this would warrent a C3, but due to the situation would you rate it as C2?

One of the main DB's is in a bedroom with a clients bed directly under it, client often in bed (I had to ask nicely for the staff to move the client so I could move the bed to access the DB). I have no idea if I should code this, if it was storage in the way I would C3 it, but in this situation? I know I would kick off if I was doing a risk assessment, but for an EICR?

May post more later.
 
Using the reminder at the end of each row from table 41.3 you can work out all your max Zs figures for 60898 and 61009. Type B is 46/In then half that for a type C, half again for a D.
Type B = 46/In
Type C = 23/In
Type D = 11.5/In

Note that this is from the BGB.
 
Using the reminder at the end of each row from table 41.3 you can work out all your max Zs figures for 60898 and 61009. Type B is 46/In then half that for a type C, half again for a D.
Type B = 46/In
Type C = 23/In
Type D = 11.5/In

Note that this is from the BGB.

Thank you, as I said earlier I am at home and all my books got left in the office as I had to rush home.
 
Just read through this post as im doing an EICR on Thursday at a garage which is the first under AMM3. I had a look around yesterday and noticed absence of RCD protection throughout so offices, workshop areas etc. As far as the condition report goes i would give all socket outlets rated at 20A or less a C2. I was surprised to see the C3 recommended for the sockets earlier in the post as i would have gone for C2 here to. Am i being harsh....?
 
Just read through this post as im doing an EICR on Thursday at a garage which is the first under AMM3. I had a look around yesterday and noticed absence of RCD protection throughout so offices, workshop areas etc. As far as the condition report goes i would give all socket outlets rated at 20A or less a C2. I was surprised to see the C3 recommended for the sockets earlier in the post as i would have gone for C2 here too. Am i being harsh....?
Yes, why do you now think it requires remedial action without delay today when last month it would have been absolutely fine and there is no requirement to retrospectively apply the regulations.
Whilst you are comparing the installation to the current regulations you are, primarily, assessing the installation for suitability for continued use, it is still suitable for continued use but improvement could be recommended.
 
Well i wouldnt have said so much the sockets in office areas until the new amendment but the sockets around workshop areas close to doors for outside use etc i would say falls under the previous amendment and wouldnt be happy leaving them unprotected....
 

Reply to Help with EICR coding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
719
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
244

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top