in that case, if it was me, i would put a 3 ph contactor on it operated by a normal switched spur
What if the 3 motors running at the same time overload the circuit. What if the customer does not want all 3 shutters opening at the same time? Does not leave the customer with many options. If there is a fault with one motor then none of the shutters will work.so the three shutters are fed from 1 mcb? the 3 core and earth are probably just control cables, why not remove 2 of the switches and put all three cables onto one switch?
Not if the problem with 1 motor was throwing the mcb. Then no motors will workthe way i understood it was the customer wanted all 3 shutters working off one switch, meaning all three opening at the same time, surely if there was a problem with one motor the other two would still work?
I may be simplifying things a little here but from what I read the OP want to isolate the roller shutters from an isolator. The shutters are on one circuit single phase. Surely just add up total load of motors and stick a DP isolator in the supply rated to cover all the load?????? Seems to be complicated for no reason.
That seems to be what the op is trying to achive, the only reson i suggested a contactor was that if this was employed then the isolator switch could be put anywhere.