if L&N are linked, you can test to E at 500v
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss HELP !! with Insulation resistance test on ring and lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Soar it would be beneficial to you to purchase these booksView attachment 6213View attachment 6214Also Guidance notes 3
mines an old Gn3 check out page 37 IR Test 2i hve gn3
With lighting circuits, in fact with any radial, it is not always apparent which is the furthest point.for the continunity of cpc (lighting) the furthest point,and do the test,but if you have two way at the stair,one switct up and one down,does that count as the furthiest point?
Not always possible, if for instance a spider configuration is used, or with spurs.i would identify the furthes point by the fact that there was only a feed in & switch wire . ( assuming loop-in at fitting scenario)
Not always possible, if for instance a spider configuration is used, or with spurs.
Also where there is two way switching, or even two way and intermediate switching some lights whislt physicaly closer to the CU, may in fact have higher R1 + R2/Zs values than fittings further away.