if L&N are linked, you can test to E at 500v
 
for the continunity of cpc (lighting) the furthest point,and do the test,but if you have two way at the stair,one switct up and one down,does that count as the furthiest point?
 
for the continunity of cpc (lighting) the furthest point,and do the test,but if you have two way at the stair,one switct up and one down,does that count as the furthiest point?
With lighting circuits, in fact with any radial, it is not always apparent which is the furthest point.
As such an R1 + R2, or Zs test at each point will determine this. Doing such will also determine correct polarity of switches.
Any switches that do not affect the readings will show reversed polarity.
 
i would identify the furthes point by the fact that there was only a feed in & switch wire . ( assuming loop-in at fitting scenario)
 
i would identify the furthes point by the fact that there was only a feed in & switch wire . ( assuming loop-in at fitting scenario)
Not always possible, if for instance a spider configuration is used, or with spurs.
Also where there is two way switching, or even two way and intermediate switching some lights whislt physicaly closer to the CU, may in fact have higher R1 + R2/Zs values than fittings further away.
 
agreed if spider or spurs, but in a standard loop in lighting radial ( talking mainly domestic ) the furthest point will be the one without a feed going out from the fitting, irrespective of how physically close to the CU it is.
 
Not always possible, if for instance a spider configuration is used, or with spurs.
Also where there is two way switching, or even two way and intermediate switching some lights whislt physicaly closer to the CU, may in fact have higher R1 + R2/Zs values than fittings further away.


Good point, because that is the answer i was waiting for, i have a two way switch and the reading is highter than the furthest point,
 

Reply to HELP !! with Insulation resistance test on ring and lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
904
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top