Help with Low insulation resistance reading | on ElectriciansForums

Discuss Help with Low insulation resistance reading in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 29, 2022
Messages
71
Reaction score
33
Location
Cork
Hello everyone,

Hope you're all well.

I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did recently. I joined all 3 phase together to neutral and tested from the busbar to earth.

I'm getting a reading of 1.33MOhms, and here in Ireland, we require a minimum of 2Mohms. I had disconnected the surge protection device previous to that. It is all RCBOs for lighting and sockets. A couple of 3 phase mcbs feeding coffee machine and oven but no appliances plugged in.

When I turned off all the mcbs and rcbos and tested busbar to earth again, I'm still getting the same reading of 1.33Mohms. Any idea what could be causing this? Is it something in circuit? Because I do have many lamps, leds etc in circuit. Is it best to disconnect all of these, which would be a monumental pain in the hole, or should the 3 phases together to neutral not negate that?

Thanks all.
 
Did you try at 250V and 500V? If they differ by a lot then you still have a SPD to E somewhere. It could be a permanently wired bit of equipment like a boiler, etc, where you don't have (or did not find) an all-pole isolator for it.

Switching off the SP/TP MCBs might isolate some circuits and help find dodgy cable or accessory, but maybe not - the L might be energised via a load (like a lamp) from the N-E voltage you apply. To really find a culprit you need to disconnect the related N each time and test it plus the related MCB-isolated L
 
Last edited:
Do the RCBOs have functional earth connections? If so you may be testing through the electronics inside the RCBO.

Find the culprit or culprits remove from the equation do another global test if okay look into the disconnected culprit/s.
Have you tried testing them separately rather than joined together, to see which one is the low one? If it's a new install then the IR seems very low.
Do the RCBOs have functional earth connections? If so you may be testing through the electronics inside the RCBO.
Did you try at 250V and 500V? If they differ by a lot then you still have a SPD to E somewhere. It could be a permanently wired bit of equipment like a boiler, etc, where you don't have (or did not find) an all-pole isolator for it.

Switching off the SP/TP MCBs might isolate some circuits and help find dodgy cable or accessory, but maybe not - the L might be energised via a load (like a lamp) from the N-E voltage you apply. To really find a culprit you need to disconnect the related N each time and test it plus the related MCB-isolated L
Hi all.

Thanks for taking the time to help and respond to me.

I sorted the issue. A 3 phase oven circuit was causing the low IR reading. The oven cable was tied into my 3 phase isolator, but I did have the isolator turned off. I'm assuming the element was throwing off my reading?
Or as pc1966 said that the L might have been energised from voltage put through on N+E?

I must add that the guys supplying all the kitchen equipment did say to me a week ago to power up that oven first and check is it working as it is second hand. I'm beginning to question if the oven could be faulty too.
 
The oven cable was tied into my 3 phase isolator, but I did have the isolator turned off. I'm assuming the element was throwing off my reading?
If the isolator is only isolating the phases (as many rotary isolators do) then reading N-E right through to a damp or faulty element would pull down your global IR reading.

Especially if it’s a 2nd hand oven that may have been sitting around for months.

Well done for finding it.
 
If the isolator is only isolating the phases (as many rotary isolators do) then reading N-E right through to a damp or faulty element would pull down your global IR reading.

Especially if it’s a 2nd hand oven that may have been sitting around for months.

Well done for finding it.

I could be wrong, but have a funny feeling that regulations in IE require that 3 pole isolation is used and neutral shouldn't be broken. Perhaps this only applies to the main isolator or perhaps it doesn't apply at all...
 
I could be wrong, but have a funny feeling that regulations in IE require that 3 pole isolation is used and neutral shouldn't be broken. Perhaps this only applies to the main isolator or perhaps it doesn't apply at all...
I want to create a new code for that:
PI : Potentially Interesting
 
Pretty certain I only ever see 3 pole main switches with removable neutral link. Maybe OP or @Risteard can confirm or make me look foolish 😂
You need a special switch if you want to switch 3 P and N - one where the neutral contact is set back so it closes early and breaks late, relative to the 3 phases.
 
You need a special switch if you want to switch 3 P and N - one where the neutral contact is set back so it closes early and breaks late, relative to the 3 phases.

4 pole main switches are fairly common here, but the point was more about the fact we're free to use them, whereas I believe they can not be used in IE.
 

Reply to Help with Low insulation resistance reading in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
340
  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
306

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top