Help with Oven Circuit. | on ElectriciansForums
Discuss Help with Oven Circuit. in the UK Electrical Forum area at ElectriciansForums.net
M
makken
Have an existing oven circuit 6mm2 twin & earth from the consumer protected by a 32a mcb goes to a cooker control switch, then 6mm2 from the switch was hardwired in to previous oven. Just bought a brand new oven (single oven that fits in cupboard under worktop) specifications are 2.3kW total electric consumption, max cable length 2m, it specifies for the cable type 3 x 1.5mm2 or equivalent.
Is it ok to wire this one the same 6mm2 straight in to the back of the oven?
16A. If the oven has a plugtop on it, you could just terminate the old 6mm to the cooker into a single socket, thus leaving the circuit and fuseboard intact, as well as the oven, as the 13a fuse in the plugtop will provide the protection.
BUT.... You could argue that if you hard wire a 1.5mm2 flex into a cooker switch/outlet, then this is part of the circuit so a lower rated MCb will be required to protect the Cable not the appliance
I agree except that he's been told to use 3x 1.5mm cable to connect the oven. If he can't get the 6mm into the oven connections, should we not also protect this bit of the cable too?
The OP asked if the 6mm could go directly into the oven, the 3x1.5mm is the recommended minimum cable size and was not in this case intended to be used.
Reply to Help with Oven Circuit. in the UK Electrical Forum area at ElectriciansForums.net
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Thanks so much for all the responses guys! It seems that what I'm planning is nothing unusual or regs-busting. I'll hook it all up and have a...