Have an existing oven circuit 6mm2 twin & earth from the consumer protected by a 32a mcb goes to a cooker control switch, then 6mm2 from the switch was hardwired in to previous oven. Just bought a brand new oven (single oven that fits in cupboard under worktop) specifications are 2.3kW total electric consumption, max cable length 2m, it specifies for the cable type 3 x 1.5mm2 or equivalent.
Is it ok to wire this one the same 6mm2 straight in to the back of the oven?
 
The circuit terminates at the outlet plate.

Thereafter follow MFI and the appliance, its cables and components will be protected by its own fuses/trips etc

The ovens that I have installed over the years have all stated a size for the MCB based on the load of the unit, this has generally been either 16 or 20Amps.
I am in complete agreement that he should check with the MFI.
 
The ovens that I have installed over the years have all stated a size for the MCB based on the load of the unit, this has generally been either 16 or 20Amps.
I am in complete agreement that he should check with the MFI.
I would agree the manufacturers may well have specified a different requirement, with which compliance would be required.

I would have thought most ovens could run on a 16/20A breaker.

However I think we have now lost the OP.
 
The exact technical data according to the manual, Voltage 220-240V 50Hz, Total Electric Consumption 2.3kW, Fuse Protection min. 13A, Cable Type/cross Section H05VV-FG 3 x 1.5 mm2 or equivalent, Cable Length 2m. Also states to a double pole control unit with a minimum contact clearance of 3mm in all poles and further stated that Additional protection by a residual current circuit breaker is recommended.

When the manufacturers manual states 1.5mm2 cable, does that mean 1.5mm2 from the consumer unit as most existing cooker circuits are surely going to be wired in 6mm2 (as mine is) or 10mm2.

Should it be wired on the rcd protected side of the consumer?

Anyway i couldn't get the 6mm2 in the cooker terminals so i rewired from the cooker switch in 2.5mm2, so the current circuit is 32a breaker (not on the rcd protected side), 6mm2 T+E to double pole cooker switch (not plug socket type) then 2.5mm2 from cooker switch to cooker terminals.

Could someone clarify if my current circuit is ok and if not what would be the ideal circuit given the specifications i have given.
 
For me I would fuse down to protect the smallest cable. We could go on about unfused spurs and minimum distances etc however where is the cable most likely to receive mechanical and damage through external influences?

As it is a dedicated circuit for one appliance (any socket on the cooker switch?) I would go with 16A MCB (20A if socket fitted). Seems strange they have stated a minimum fuse size but no maximum???
 
Yeah they state the minimum fuse size, and then you have to select the cable to suit.

Personally I would go into the oven with 3 core 2.5mm flex, heat resistant stuff would be great to use as well.
Then I'd change the mcb for a 20A one.
 
Hmmm, there seems to be varied opinions on what one would do, would i be right in assuming there are different ways to do this and still have a perfectly safe circuit, also what about the manual stating additional protection with an rcd.
 
The exact technical data according to the manual, Voltage 220-240V 50Hz, Total Electric Consumption 2.3kW, Fuse Protection min. 13A, Cable Type/cross Section H05VV-FG 3 x 1.5 mm2 or equivalent, Cable Length 2m. Also states to a double pole control unit with a minimum contact clearance of 3mm in all poles and further stated that Additional protection by a residual current circuit breaker is recommended.

When the manufacturers manual states 1.5mm2 cable, does that mean 1.5mm2 from the consumer unit as most existing cooker circuits are surely going to be wired in 6mm2 (as mine is) or 10mm2. This is specifying the cable from the fixed wiring to the cooker, the one specified is a 3 core flex. Run from the CU would cause problems with the 2m limit, they are trying to ensure that the cable will not over heat.

Should it be wired on the rcd protected side of the consumer? Since the manufacturers recommend it then it should be RCD protected, there may be other requirements in the wiring regulations that mean an RCD must be present, but this would get beyond a simple cooker replacement and start to involve the requirements of the Building regulations, testing and certification of the work and notifying building control as well.

Anyway i couldn't get the 6mm2 in the cooker terminals so i rewired from the cooker switch in 2.5mm2, so the current circuit is 32a breaker (not on the rcd protected side), 6mm2 T+E to double pole cooker switch (not plug socket type) then 2.5mm2 from cooker switch to cooker terminals.

Could someone clarify if my current circuit is ok and if not what would be the ideal circuit given the specifications i have given. An ideal circuit would be a 2.5mm2 twin and earth cable run direct from a 16A RCBO in the CU to a double pole switch (whether fused at 13A or not) and from the double pole switch to the cooker in HO5VV-F flex at either 1.5mm or 2.5mm.
See my comments in your quote above.
As Cbw says the fixed wiring is up to the outlet point so theoretically your circuit is suitable so long as all other requirements for the load / wiring regulations are maintained.
As said above you could fuse down to 13 at/ in place of/ just after the Cooker switch.

The cooker switch meets the 3mm contact gap requirement, as would a double pole FCU.

Please remember that since we have not seen the installation, instruction manual or cooker in reality, we can only give information based on what you have said and the information we give may not be correct.
 

Reply to Help with Oven Circuit. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K
  • Question
Thanks so much for all the responses guys! It seems that what I'm planning is nothing unusual or regs-busting. I'll hook it all up and have a...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top