Hello all
Am trying to calculate suitability of using swa armouring as c.p.c. It is a 6mm 2c supplying a log cabin.
From table 54.7 the calculation I need to use to find min csa of armouring is (k1/k2) x S
Taking value from table 43.1 for 90c cable I have k1 = 100 and K2 = 46 (Table 54.4)
So (100/46) x 6 = 13 which is my min CSA size of cpc. My question is where do I find the CSA of 6mm 2C cable and also does the type of supply need to be taken into account at all if either tns or tncs my understanding is that this doesn't. Any help appreciated.