Help with test results. | on ElectriciansForums
Discuss Help with test results. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
E
electek
Hi , Just aquired a 2nd hand tester (Robin kts 1620) and decided to do a few tests around my house , now i know this system is TT and has a 100mA rcd unit fitted before the CU , The CU has just a main switch ( no rcd ) and circuit breakers.
Here are test results carried out on RFC (There are appliances plugged in on this circuit)
earth loop impedance
20 ohm range - overload , 200 ohm range - 25.4 ohms , 2000 ohm range - 31 ohms
Here are the test results carried out on a ceiling rose in a bedroom
20 ohm range - 0.04 ohm , 200 ohm range - 3.2 ohms , 2000 ohm range - overload.
Can anyone help me with these test results
This is just speculating a bit.i dont know the meter
This may be possible with a two lead tester
The ring circuit has a sound insulation value, between neutral and earth,so the readings reflect the TT expected
The lighting has a low neutral earth insulation value (not enough to imbalance the 100m/amp rcd but enough to affect the results) what you are reading may be more an earth loop reading down the neutral of the supply
Hi , just done an earth rod resistance test and found it to be open circuit ! suspect the earthing to be through the earth clamp on the water piping ! I know this isn't right and looks like i need a new earth electrode. However the earth resisitance through the water pipe was between 25 ohms and 80 ohms depending on which setting i use on the tester - why does the tester give such differences in resisitance on the different ranges i.e 20 ohm , 200 ohm and 2000 ohm ?
What is the maximum Ze (through the earth rod) on a tt system ?
Reply to Help with test results. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Good point James. It would have been nice if the manual had mentioned which of the leads were being used for what though. It simply shows the LNE...