Help with tt system certification | Page 2 | on ElectriciansForums
Discuss Help with tt system certification in the Australia area at ElectriciansForums.net
Simon81
HiCan anyone help me with regards to filling in a niceic part p cert with regards to the part were it concerns tt.This is on page 2 I need help with the parts electrode resistance ra , is this the measured ze result I have taken ?And also method of measurement ? Also what is the maximum ze for a tt system , I no it's 0.35 for tncs and 0.80 for tns. Any help is appreciated Thanks
I've got some sympathy for the OP here.
The OSG defines limitations for TNCS and TNS very well but when it comes to TT is less than clear having 200 ohms or 100 ohms for the Re/Ra doesn't help. When it comes to main bonding its the same ambiguity.
Lets hope such "details" are clearer when the next edition of the OSG comes out.
For what its worth I'm with the NICEIC to aim for sub 100 ohms, and I'd like to see main bonding brought into line with TNCS and TNS too.
Tin hat on!
Once again Simon I apologise for the tone of my post,although I stand by the gist of what I was trying to say.
At least you have asked for the correct information,rather than fabricating a cert in the pub which is what a lot of blokes would do if they didnt know....(and even if they do know)
Thanks formal your replys got a ze of 4.69 just had a nightmare with it all. Also I have been told to enter 0.2 in the disconnection time and have been given the following maximum zs for the following mcb 6amp 38.3316amp 14.3820 amp 11.5032amp 7.19Does anyone no if this is right?
trhe bit in red is gibberish. ok.?
Tin hat on!
But look what he posted above regarding maximums for devices, that was just a lack of basic knowledge, never mind TT specifics!
I've got no sympathy whatsoever, he could be installing this at my mother's house!
How can we all bang on about competency and sliding standards then defend posts like this one?
If the post had started "I'm doing a TT system next week, I have a few questions.......
I am a compotent electrician I no the maximum zs for mcb 32 1.44 6 7.67 etc but I have been told by a fully approved niceic member that the values change when the system is tt so is he wrong is that what your saying
Not wishing to be too critical, but your posts would benefit from some punctuation, and editing, before you hit the "post" button
As far as im aware the max zs of the device never changes,but with it being a TT system you are more than likely going to be over the max zs when testing.There are tables in the brb that you can look at to see if they are ok.Think its table 41.5,i may be wrong as i dont have my book handy at the moment,but someone may point you in the right direction.
Them values that I have been given are from nic software so who wrong?If the values don't change how can a ze of 4.69 and a r1 + r2 of 0.68 which gives a zs of 5.37 be within the maximum zs of a 32 amp mcb 1.44 ????
Not wrong no but, it's the introduction of RCD's to cover earth fault protection due to the high Zs values that effect the changes in maximum permitted values i.e. 1667ohms for a 30mA RCD etc etc.
Reply to Help with tt system certification in the Australia area at ElectriciansForums.net
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...