Hi all I am about to start pricing up my first big job. 6 Bedrooms, 4 bathroom/shower rooms , 2 receptions, Utility room, Kitchen diner.
I would like to ask some of the more knowledgeable on here for advice regarding certain things, so thought like Wade did a few months ago keep it all to one thread.
Circuit wise I was going to split it like this.
1: Bedroom Power 32 amp 20 Twin Skts
2: Bedroom Lighting 6 amp 6 Points
3: Bathroom and shower room Lighting 10 amp 21 points including extraction
4: Reception, Hall, stairs and landing power 20 amp 15 Twin skts
5: Reception, hall, stairs and landing lighting 6 amp 15 points including 4 No5amp lighting points
6 Kitchen and utility lighting 10 amp 14 Points
7:Kitchen diner and utility power 32 amp 7 twin skts
8: garden lighting 10 amp ?
9: Shed power and lighting 20 amp ?
10: Cellar power and lighting 20 amp 7 Points
All light fittings are going to be standard pendants except in the kitchen, bathroom and shower areas.
With diversity calcualted I make that 114 amp maximum load, would that be correct?
This hasn't taken into consideration any kitchen appliance rated over 2kw or the 4 Electric fires they are fitting.
Could I install a separate radial just for the Electric fires as they could be rated 2kw or greater. They are being fitted in existing chimney breast so was thinking spur outside to a single socket behind to plug into? Thus not allowing any thing else to be plugged into circuit.
I am still awaiting the spec on the kitchen appliances so may get away with putting them on the local power circuits, if so I would consider splitting them into 2 circuits.
Many thanks
I would like to ask some of the more knowledgeable on here for advice regarding certain things, so thought like Wade did a few months ago keep it all to one thread.
Circuit wise I was going to split it like this.
1: Bedroom Power 32 amp 20 Twin Skts
2: Bedroom Lighting 6 amp 6 Points
3: Bathroom and shower room Lighting 10 amp 21 points including extraction
4: Reception, Hall, stairs and landing power 20 amp 15 Twin skts
5: Reception, hall, stairs and landing lighting 6 amp 15 points including 4 No5amp lighting points
6 Kitchen and utility lighting 10 amp 14 Points
7:Kitchen diner and utility power 32 amp 7 twin skts
8: garden lighting 10 amp ?
9: Shed power and lighting 20 amp ?
10: Cellar power and lighting 20 amp 7 Points
All light fittings are going to be standard pendants except in the kitchen, bathroom and shower areas.
With diversity calcualted I make that 114 amp maximum load, would that be correct?
This hasn't taken into consideration any kitchen appliance rated over 2kw or the 4 Electric fires they are fitting.
Could I install a separate radial just for the Electric fires as they could be rated 2kw or greater. They are being fitted in existing chimney breast so was thinking spur outside to a single socket behind to plug into? Thus not allowing any thing else to be plugged into circuit.
I am still awaiting the spec on the kitchen appliances so may get away with putting them on the local power circuits, if so I would consider splitting them into 2 circuits.
Many thanks