Hi, can anyone offer any advice as to why the heating would run when HW is called for? | on ElectriciansForums

Discuss Hi, can anyone offer any advice as to why the heating would run when HW is called for? in the Central Heating Systems area at ElectriciansForums.net

Joined
Oct 29, 2019
Messages
8
Reaction score
2
Location
England
Hi, can anyone offer any advice as to why the heating would run when HW is called for?[ElectriciansForums.net] Hi, can anyone offer any advice as to why the heating would run when HW is called for?
 

Attachments

  • [ElectriciansForums.net] Hi, can anyone offer any advice as to why the heating would run when HW is called for?
    15969587125327018771546125567166.jpg
    77.1 KB · Views: 26
Hi thanks for your message. There is not a valve on this system. It looks like it uses the double pole relay, It is a very old system. 1978 it was installed

Based on the wiring center diagram you've posted you have a conventional system boiler.

You will have one, two (or even 3) zone valves as per the pictures bellow.
[ElectriciansForums.net] Hi, can anyone offer any advice as to why the heating would run when HW is called for?

[ElectriciansForums.net] Hi, can anyone offer any advice as to why the heating would run when HW is called for?
 
Hi thanks for your message. There is not a valve on this system. It looks like it uses the double pole relay, It is a very old system. 1978 it was installed
Surely there still has to be some sort of a motorised valve to close the heating circuit. If not then you will always have heating when the boiler fires.
 
Based on the wiring center diagram you've posted you have a conventional system boiler.

You will have one, two (or even 3) zone valves as per the pictures bellow.

No, the wiring diagram posted does not show a conventional system boiler with zone valves.

The wiring diagram posted shows a 2 pump system utilising a DPDT relay. The biggest clue to this is 'two pump system' written on it.
[automerge]1596964186[/automerge]
Surely there still has to be some sort of a motorised valve to close the heating circuit. If not then you will always have heating when the boiler fires.

According to the picture it is a two pump system, no motorised valves are used with this.
[automerge]1596964649[/automerge]
Hi, can anyone offer any advice as to why the heating would run when HW is called for?

It is impossible to say from just that diagram.

Haa it always worked this way or is it a fault which has developed recently?

Does the room thermostat have any effect when the CH has come on via the hot water controls?

Unfortunately the wiring diagram is incomplete, it doesn't show the internal links between the connections so we can only guess at what the full circuit is.

Without further information this needs to be tested by a good electrician.
 
Last edited by a moderator:
No, the wiring diagram posted does not show a conventional system boiler with zone valves.

The wiring diagram posted shows a 2 pump system utilising a DPDT relay. The biggest clue to this is 'two pump system' written on it.
[automerge]1596964186[/automerge]


According to the picture it is a two pump system, no motorised valves are used with this.

I apologies, your right, I didn't look closely enough at the diagram to see the second pump. I didn't even know such a system existed, I've seen gravity hot water but never a second pump.

Surely without a valve both systems will always heat up?
[automerge]1596964910[/automerge]
No, the wiring diagram posted does not show a conventional system boiler with zone valves.

The wiring diagram posted shows a 2 pump system utilising a DPDT relay. The biggest clue to this is 'two pump system' written on it.
[automerge]1596964186[/automerge]


According to the picture it is a two pump system, no motorised valves are used with this.
[automerge]1596964649[/automerge]


It is impossible to say from just that diagram.

Haa it always worked this way or is it a fault which has developed recently?

Does the room thermostat have any effect when the CH has come on via the hot water controls?

Unfortunately the wiring diagram is incomplete, it doesn't show the internal links between the connections so we can only guess at what the full circuit is.

Without further information this needs to be tested by a good electrician.

If there are no valves in the system a blockage in the hot water flow/return may well force flow through the heating circuit instead.
 
I apologies, your right, I didn't look closely enough at the diagram to see the second pump. I didn't even know such a system existed, I've seen gravity hot water but never a second pump.

Surely without a valve both systems will always heat up?

No, or not to any significant extent. With one pump running and the other not the vast majority, if not all, of the hot water will be circulated by the running pump and not get through the stationary pump. This assumes the system is properly designed.

There is a possibility of heat creeping via the return pipe, but good pipework design should combat this, or a non return valve.
[automerge]1596965220[/automerge]
If there are no valves in the system a blockage in the hot water flow/return may well force flow through the heating circuit instead.

I doubt that this would cause enough flow through the heating to make it appear to be on, maybe slightly warm at best.

A blockage in the hot water pipework will cause the hot water pump to be pumping against the blockage, this won't normally cause any water to flow via the heating pump.
 
This is the old wiring centre, we assume it has always worked correctly. Please not that on the picture if there is a notch then the terminals have a link. We have rewired the property but kept the heating system as was just renewing the cabling. Could the frost stat cause an issue if set to call for heat?
 

Attachments

  • [ElectriciansForums.net] Hi, can anyone offer any advice as to why the heating would run when HW is called for?
    15969667078218460042569075887911.jpg
    100.4 KB · Views: 25
This is the old wiring centre, we assume it has always worked correctly. Please not that on the picture if there is a notch then the terminals have a link. We have rewired the property but kept the heating system as was just renewing the cabling. Could the frost stat cause an issue if set to call for heat?

Ah, so you are an electrician working on the system, your OP gave the impression of a fault finding situation on an existing installation, not that you'd interfered with the wiring and messed it up.

My first question has got to be why did you mess with a working system?

Did you not take the time to investigate and understand the control system before you took it apart?

Did you test the system before taking it apart to ensure you understand how it is supposed to work and whether or not it was working correctly?

You have the old wiring centre and the wiring diagram so you can work backwards from this to draw yourself a diagram of how it was connected previously. From this you can work out how the system is supposed to work and then start to fault find.
[automerge]1596969169[/automerge]
Do you have a diagram of exactly how you have connected the new wiring for this system?

Without that the most we could possibly do is draw a diagram of how it was originally wired, but that won't help explain why it is not working now.
 
Last edited by a moderator:
Ah, so you are an electrician working on the system, your OP gave the impression of a fault finding situation on an existing installation, not that you'd interfered with the wiring and messed it up.

My first question has got to be why did you mess with a working system?

Did you not take the time to investigate and understand the control system before you took it apart?

Did you test the system before taking it apart to ensure you understand how it is supposed to work and whether or not it was working correctly?

You have the old wiring centre and the wiring diagram so you can work backwards from this to draw yourself a diagram of how it was connected previously. From this you can work out how the system is supposed to work and then start to fault find.
Thanks for your message.

My mistake was not confirming how the system worked and if it worked correctly. We had to rewire the system as all cabling did not have any cpc's and the original install was installed very poorly. I have done as you suggest and worked backwards and cannot see any immediate issue with the design of the system. Hence I am looking for another input from electricians. Thanks for taking time to reply to this thread. I assume you don't have any advice as requested ?
 
Thanks for your message.

My mistake was not confirming how the system worked and if it worked correctly. We had to rewire the system as all cabling did not have any cpc's and the original install was installed very poorly. I have done as you suggest and worked backwards and cannot see any immediate issue with the design of the system. Hence I am looking for another input from electricians. Thanks for taking time to reply to this thread. I assume you don't have any advice as requested ?

Do the pumps stop and start in response to demand from the two thermostats/time clock?

If you connect a switched live to the boiler and temporarily connect power the pump bypassing the controls does the issue go away?

If you fire the boiler and run only one pump and the other circuit heats up that would imply its a piping design/plumbing fault rather then a an electrical issue.

Heating systems used to be entirely gravity fed using only the fact cold water is more dense than hot water. It may be your getting effects such as these.
 
Last edited:
Do the pumps stop and start in response to demand from the two thermostats/time clock?

If you connect a switched live to the boiler and temporarily connect power the pump bypassing the controls does the issue go away?

If you fire the boiler and run only one pump and the other circuit heats up that would imply its a piping design/plumbing fault rather then a an electrical issue.

Heating systems used to be entirely gravity fed using only the fact cold water is more dense than hot water. It may be your getting effects such as these.
Thanks for your message. I am back on the job tomorrow. I will what you have suggested ?
 
Thanks for your message.

My mistake was not confirming how the system worked and if it worked correctly. We had to rewire the system as all cabling did not have any cpc's and the original install was installed very poorly. I have done as you suggest and worked backwards and cannot see any immediate issue with the design of the system. Hence I am looking for another input from electricians. Thanks for taking time to reply to this thread. I assume you don't have any advice as requested ?

So can you post the wiring diagram you have created of the old system? Or describe its operation?
Can you also post the wiring diagram of what you have installed?

You haven't given enough information to be able to offer any helpful advice as far as I can see.

A diagram of what you have installed will allow us to see how it is currently operating and suggest how to achieve the desired operation.

I have given all the advice I can confidently give without further information.
I could offer you a bunch of random guesses at what might be wrong, but that wouldn't help.
 

Reply to Hi, can anyone offer any advice as to why the heating would run when HW is called for? in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

E
  • Article
Can a HW cylinder be used as primary heat source for CH only? Hi, I would like to know if a HWC can be used as a primary heat source for a new...
Replies
0
Views
184
eric12
E
K
  • Article
Main 24HE constantly cutting out and firing back up on HW and Heating and intermittent flame failure light. I am having a problem with my main...
Replies
0
Views
218
keyplayer
K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top