Hi...great forum, looking for some help...

I have a MK Sentry Consumer Unit box, fitted in my home, normal residential load, around 1984, containing a 4-module LN 5780 ELCB 80A 30ma. This is regularly tripping when a new load is applied, for example switching a random light or power load on, suggesting it needs to be replaced. I understand the design of MK Sentry modules was subject to a design change, meaning newer RCD units are no longer compatible with my box. So I figure the most cost effective solution is to completely disconnect the ELCB and replace it with a new MK external 4-module enclosure containing a 100A isolation switch and latest model MK 80A 30ma RCD. Run the existing meter tails into the new enclosure and new meter tails into the old enclosure.
Does this make sense?

With regard to the old ELCB I would like to do this right and completely remove it but I'm not sure I can get suitable blanks to fill the 4 module spaces. Any suitable blanks I can get hold of? Alternatively I could leave it in place and simply put a sticky label over it with the words..."Faulty, completely disconnected from the load" ...or similar. Would that pass an inspection?
Thanks.
 
Can a Surge Protect Device cause RCD problems?

This problem has become so annoying that I have spent a rainy w/e carefully investigating, collating and comparing my findings with past experience, and I am now doubting my initial analysis.

Problem only ever occurs when my computer rig is powered up and in-circuit. This consists of a variety of devices all supplied through a master switch which is in turn connected to power through a SPD All devices are left with their individual power switch on, so hitting the master switch powers everything up simultaneously.
Switching the computer rig on may cause a power trip, but not always. Most times it happens after powering the computer rig on and then shortly after powering some other load on. At that point (when the power trips) it can only be restored when the computer rig is removed from power entirely.
In the past the power trip happened when I switched the computer master switch off. At that time I renewed the SPD and the problem disappeared for about 1 year, only to return with the onset of autumn and the house fully loaded in the evening.
So my question at the top?
 
So long as the old ELCB is labeled as no longer being connected I can't see a problem. However, for all the messing about, I would consider changing the 30 year old consumer unit for a new split load consumer unit which has 2 RCD's so that you only lose some of the circuits if one of the RCD's operate.
 
The fact that you have an RCD that trips is not usually indicative of a faulty RCD but is indicative of a fault on one of the circuits it protects.
Even though it is old it is probably still doing its job and protecting you from potential electric shock.
It would be best to check the circuits for faults first before you spend lots of money changing something that may be working.
 
Thanks, good advice. I just spent a rainy w/e investigating this in depth...

Can a Surge Protect Device (4-way extension lead) cause RCD tripping.

After collating lots of RCD trips I established that it only happens when my computer rig is powered up. Sometimes powering up the computer trips the power, in the past powering it down would trip it but that no longer happens. Typically I power up the computer, and then sometime after power up another load and the power trips. Tried isolating individual devices in the computer rig but trips continue. The only common factor is the SPD, the power light of which is continually flickering. So I'm off the B&Q.
 
The fact that you have an RCD that trips is not usually indicative of a faulty RCD but is indicative of a fault on one of the circuits it protects.
Even though it is old it is probably still doing its job and protecting you from potential electric shock.
It would be best to check the circuits for faults first before you spend lots of money changing something that may be working.

Yes, very good point.

You may need to get help with the testing if you don't have access to an insulation resistance tester and experience of how to conduct the tests.
 
Hi...great forum, looking for some help...

I have a MK Sentry Consumer Unit box, fitted in my home, normal residential load, around 1984, containing a 4-module LN 5780 ELCB 80A 30ma. This is regularly tripping when a new load is applied, for example switching a random light or power load on, suggesting it needs to be replaced. I understand the design of MK Sentry modules was subject to a design change, meaning newer RCD units are no longer compatible with my box. So I figure the most cost effective solution is to completely disconnect the ELCB and replace it with a new MK external 4-module enclosure containing a 100A isolation switch and latest model MK 80A 30ma RCD. Run the existing meter tails into the new enclosure and new meter tails into the old enclosure.
Does this make sense?

With regard to the old ELCB I would like to do this right and completely remove it but I'm not sure I can get suitable blanks to fill the 4 module spaces. Any suitable blanks I can get hold of? Alternatively I could leave it in place and simply put a sticky label over it with the words..."Faulty, completely disconnected from the load" ...or similar. Would that pass an inspection?
Thanks.

What testing have you carried out to confirm that the existing RCD is faulty?

The symptoms you describe sound more like those of a neutral to earth fault than a faulty RCD.
 
I appear (so far) to have solved this. There were 2 x SPD 4-way strips in the power supply circuit for the computer rig. The kind that have a green light indicating the SPD function is operational and a red light indicating the power is on. On one of them the green was very dim and red constantly flickering. Took both out and rewired the complete circuit with non-SPD strips and a single good quality SPD plug from Screwfix, mounted right next to the master switch so it can be easily removed from the circuit for testing. I also found an external floodlight which was badly deteriorated due to the weather, and may have contributed to the problem since switching that circuit on regularly caused the trip (as long as the computer rig was powered up, cumulative residual currents?). Now replaced with a LED flood. So far no more trips.
Thanks for the advice. Good for my wallet also since MK (the complete DB is MK) responded to my enquiry advising that I replace the entire DB.
 

Reply to Hi, need some help with a MK Sentry Consumer Unit problem. in the The Welcome Forum area at ElectriciansForums.net

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
693
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

Search Electricans Forums by Tags

Tags Cloud - Most Used Words - Use them to search for topics

110v 12v 17th 17th edition 18th 18th edition 2 way 2330 2365 2391 240v 3 phase 6mm access account across adding additional advice advise after again alarm alarms always am2 amendment amp another answer anybody anyone anything appliance appliances application apply apprentice apprenticeship approved area arial armoured around assesment assessment attach aus ausie elec available basic bathroom batteries battery because become becoming becsa before being bell best better between black block blowing board boards boiler bonding book books bosch box boxes brand breaker breakers british bs7671 bsi build builder building bulb bulbs business button c&g cable cable size cables calculation calibration camera can't canada car caravan card career cctv ceiling central central heating cert certificate certificates certification certs certsure change changes changing charge charger charging cheap check cheers christmas circuit circuits clamp class code codes college combi coming commercial companies company competent complete condition conductor conductors conduit confused connect connected connecting connection connections connector connectors consumer consumer unit contact contactor content continuity contract contractor control controller conversion cooker copper core correct cost council couple course courses cover cpc cps crabtree cupboard current customer customers dead deal degrees demand design details detector device dewalt diagram difference different dimmer dimmer switch dimmers distribution diversity diy dno doing domestic domestic installer don't door double downlight downlighters downlights drill driver earth earth rod earthing east economy economy 7 ecs edition eic eicr elecsa electric electrical electrical installation electrical nvq electrical tools electrical wiring electrical work electrician electricians electricians london electricians mate electricians vans electricity electrics electriians mnchester element email emergency emergency lighting employed energy engineer engineering enough entry equipment essex every everyone exam existing experience extending extension external extra extractor extractor fan fan fans fault fault finding faulty fcu final finding fire fire alarm first fit fitted fitting fittings fixed flat flats flex flickering floor fluke fluorescent for sale forms forums found free fuse fused fused spur fuses garage garden gas generator get getting going great green grid ground gu10 guidance guide guilds hager halogen happy having heat heater heaters heating hello help help please help! hi everyone hnc hob home honeywell hot tub hours house how to ideas immersion impedance improver in london incoming induction industrial industry information infraction inside inspection inspection and testing install installation installations installed installer installers installing insulated insulation insulation resistance insurance interesting intro introduction inverter inverters isolation isolator issue issues jib jib card job jobs joining junction keeps kewtech kit kitchen knowledge lamp lamps large lead leads leakage led length lenny level level 2 level 3 light light switch lighting lighting circuit lights little live load local location loft london long looking looking for work loop low voltage ltd machine main main switch mains maintenance makita manchester manual mate max maximum mcb mcbs mcs media megger member members message metal meter meter tails meters method metrel mft might minor missing mobile module money motor mounted mounting moving multi multifunction multiple murdoch myself napit need help needed needs neutral never new new build new member newbie niceic night no earth north not uk not working notifiable number nvq off offer office old online opinions options other out outbuilding outdoor outlet outlets output outside oven overload panel panels parallel part part p passed pat pat testing people periodic person pfc phase phone pipe pir place plan plastic plate please plug plumbing advice pme point points pole position possible post posts power practical practice price prices pricing private problem problems project property protected protection protective pump pvc qualification qualifications qualified quality query question questions quick quote radial range rated rates rating rcbo rcbo's rcbos rcd rcd tripping rcd's rcds reading readings really recommend recommendations red regarding registered regs regulations relay remote repair replace replacement replacing required requirements resistance results rewire right ring ring final ring main roman roof room rose running safe safety salary sale saying scheme scotland screwfix sds second section security self self employed sensor series service services shed shock short shower simple single single phase site plan size sizing skills sky small smart smoke smoke alarms socket sockets software solar solar panel solar pv someone something sorry source south spark sparks sparky split spur spurs standard start starter starting steel still storage storage heater strange strip students stuff sub main suggestions supplier suppliers supplies supply supply to surge swa switch switched switches switching system systems t&e table tails taking terminal termostat test tested tester testers testing tests thank the forum their thermal thermostat these thing things thinking those though thought thoughts thread three three phase through time timer times tips today too tool tools trade trainee training transformer transformers trip tripped tripping trips trunking trying tt system type under underfloor underfloor heating unit units update upgrade urgent used using value values valve van vehicle video volt drop voltage voltage drop volts wall wanted warning water weeks welcome west what's whats where white wind wire wired wireless wires wiring wiring help within without work working works worth wrong wylex years zone zones

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top