I wanted to know if there are any UK regs prohibiting having the fan switched so that it comes on independently of the light (ie just the fan or light or both)
 
It depends on whether you have a window in the bathroom, if you can open a window, the fan can be switched independently. If there are no windows then the fan must come on and stay on for 30 minutes after switching on the light (thats the building regs bit)...
 
It depends on whether you have a window in the bathroom, if you can open a window, the fan can be switched independently. If there are no windows then the fan must come on and stay on for 30 minutes after switching on the light (thats the building regs bit)...
I have a window in the bathroom - does this mean that a dual switch would be OK on the wall outside of the room? sorry being a bit dense but don't want to do anything wrong ☹
 
I have a window in the bathroom - does this mean that a dual switch would be OK on the wall outside of the room? sorry being a bit dense but don't want to do anything wrong ☹
A seperate light switch and fan switch is quite normal outside of a windowed bathroom. The problem will be how to wire them up correctly And the fan itself may need to be adjusted. There should be a separate isolator switch for the fan anyway, is this the case?
 
A seperate light switch and fan switch is quite normal outside of a windowed bathroom. The problem will be how to wire them up correctly And the fan itself may need to be adjusted. There should be a separate isolator switch for the fan anyway, is this the case?
yes - it's currently wired up separate to the light switch - but won't come on without the light being on which is a bit of a pain with the lighter mornings / evenings as I don't necessarily need the light on.
 

Reply to Hi - switch question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
782
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

The 2 inputs are separate and there should be no interlinking between SL1 and2 If there is there has to be a wiring error or a fault with the...
Replies
1
Views
429
Replies
2
Views
409

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top