Gringoking88

-
DIY
Joined
Jun 18, 2015
Messages
176
Reaction score
50
Location
London
Hi all,

Looking to exploit (please) those older and wiser lol. I was asked to extend / relocate a cooker circuit (6mm t&e) and did so no problems. I then started doing the minor works, R1+R2 came in at 0.05 ohms so was perfect. However, I then went to do do an Ze at the board and get very high readings e.g. around the 6 ohms Mark, this obviously resulted in my Zs being outside acceptable values.

The first learn I guess is always do a Zs / Ze before you take a job (I know, a rookie mistake)! But the question is how would you guys approach this now e.g. what would you do with the minor works, would you advise the customer to contact dno then retest or just calculate Zs from the given Ze and complete the minor works when the Ze is rectified, or would you do a minor works now, note the customer needs to rectify Ze then reissue another minor works?

Many thanks in advance,

Martin.
 
Was the main earth dissed?, had you nulled the MFT leads? what type and size was the OCPD? and it's max Zs? What is the supply system?
 
Last edited:
You now have a situation where you have altered a circuit possibly leaving it without fault protection even if there is an rcd in place. What is the "apparent" earthing system.
 
...don’t forget the bonding too!
Pete,

Yes the main earth was disconnected, yes leads mulled, 16mm main earth, it is a tn-s earthing system Max Zs should be 1.36.

Thanks,

Martin.
Try testing the Ze again Martin could have been a bad connection on your test leads, if it's round about the same then as suggested your customer needs to contact the DNO.
 
I had this once on a phase at a police station, arranged UKPN to attend, within a day they dug out the road and located a loose connection. They had a meter that could locate the fault in approx. Metres! Nice bit of kit.
 
TNS with Ze of 6 is clearly a fault for DNO to fix. You could call DNO, or have Customer call them with you standing there.
You are right that Ze should be checked before starting work, that way you could have this chat up front and get it fixed first. Now I would say "cert will be done when work is completed, and that's when the means of earthing has been restored".
Agree @westward10 not to energise a circuit with a known fault.
 
I have a question, I'm still in training and my college tutor said if a circuit fails on a Zs to stick it on an rcbo or RCD. obviously with this it's the Ze so it's the DNOs responsibility. Now is my tutor right on this? Where do you draw the line? And also what do you put on the test sheet?
 
I have a question, I'm still in training and my college tutor said if a circuit fails on a Zs to stick it on an rcbo or RCD. obviously with this it's the Ze so it's the DNOs responsibility. Now is my tutor right on this? Where do you draw the line? And also what do you put on the test sheet?
Tutor is being lazy. Think about why we need a low Ze/Zs and what effect it has upon the installation.
 
I have a question, I'm still in training and my college tutor said if a circuit fails on a Zs to stick it on an rcbo or RCD. obviously with this it's the Ze so it's the DNOs responsibility. Now is my tutor right on this? Where do you draw the line? And also what do you put on the test sheet?
When he says fails on Zs is this for an EICR or a new circuit. For a TN system you should not be relying on an rcd for fault protection. So if this is an EICR you can remedy the situation by changing the protective device for a different type or even a lower rating and as a last resort an rcd/rcbo. For a new circuit this should never happen if correctly designed. A 30ma rcd on a TN system is for additional protection, e.g. socket outlets and cables without earth containment in walls etc.
 
You’d only need a 100mA rcd/rcbo to deal with the fault protection issue on a high zs tho depending if it’s protecting socket outlets or cables buried in walls or additional protection is needed for other reasons, then 30mA will be required.
As said a new circuit on a TN system should be designed that the mcb provides satisfactory fault protection for said circuit.
 
Thanks all for the reply's!!! I also spoke to NICEIC technical helpline and they advised to exactly as Wilko said, A+ Wilko lol! I have advised customer to call DNO and given them the details of the fault etc. Said I would retest when its rectified at no cost. They seemed very happy that I actually cared and didnt just make up the certificate lol
 
Oh dear, I must've put the radio on NIC FM o_O
LOL, What I am confused about, or perhaps, I should say, there is confusion about is; if the Ze is high, some have suggested the circuit should not be energised, but this fault would affect the entire property so would you therefor not turn off the entire installation??? Not sure how the property owner would feel about that lol.
 
Yes the fault affects the whole property, but you've modified one circuit. My view is the circuit is "out of normal service" during your work (including the live tests) and by testing you know it does not meet the intended design. So the circuit should not be returned to "normal service" by you.
 
LOL, What I am confused about, or perhaps, I should say, there is confusion about is; if the Ze is high, some have suggested the circuit should not be energised, but this fault would affect the entire property so would you therefor not turn off the entire installation??? Not sure how the property owner would feel about that lol.
Yes judge I was fully aware of the possible outcome of making the circuit live knowing the earth was not satisfactory.
 
Agree with all those that state advise dno to rectify but hypothetically or technically what is the difference of a tt System with zs readings sub 200 ohms?
Edit to say c/w 30ma rcd
 

Reply to Hi Ze at distribution board, how would you approach? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
842
  • Question
Absolutely, yes. It was just a bit of a joke, looking at your quoted Z values. edit. Oh, joking too!.....I see your attempted smile didn't work ...
2
Replies
28
Views
6K
  • Question
Read up on the definitions of conductors, then circuits. Then double check what bunching is defined as - and the answer will be apparent PLUS...
Replies
1
Views
2K
  • Question
Youre in the same boat as me. I was previously with niceic and later on, napit. No issues. I didn't bother finishing my nvq3 as in 2010 during the...
Replies
7
Views
3K
  • Question
Many thanks
2
Replies
37
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks