High continuity reading when testing lighting circuit | on ElectriciansForums
Discuss High continuity reading when testing lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
M
MWE
Hi any ideas when i have conducted the cont test on a lighting circuit R1+R2= 44.5 any ideas???:confused:
Hi tester just come back from cal centre,leads are a new set and i've tested a seperate supply to a lighting circuit in the cellar with spot on readings??
IR reading of 33.9 meg (R1+Rn joined) to cpc. i know this passes but this is quite low also???
R1 + R2 should be carried out at every point on the circuit so is your reading bad from point 1 onwards or does it jump up between 2 points.
Then check between cpc's at these points with a wander lead. Could be a bad connection at a jb out of sight.
Reply to High continuity reading when testing lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
You would be best checking all connections as it is possible it is having a cumulative effect.
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch