Take out all the lamps and do it again , you could have a open circuit at a point and the reading you are getting is back feeding to the CDU via the L and N so you could be getting a reading at the CDU N and E through the lamps
 
do a continuity between point 3 and the last point. if that's ok, you know you have a fault between 2 and 3
 
hi telectrix i know i have the fault between 2 & 3 ive done the ir test on this bit of the circuit and all ok but the continuity reading is high all connections are sound what are visible,i am now thinking that there has been another connection made inbetween at some point which obviously i cant see. NIGHTMARE
 
A couple of other things to check could be any outside lights (had this the other day) spurred off the lights, anything in the loft and also has somebody spurred a socket off the lights?


Since P = V²/R = 230²/43(?)ohms i think you are looking at something that could be using in the order of 1200watts. If that was a single bad connection that would be a lot of heat and a lot of voltage dropped. Are the lights normal brightness when on ? if they are i think its a question of slowly wondering round with a cup of tea and looking for something you've missed.
 

Reply to High continuity reading when testing lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

You would be best checking all connections as it is possible it is having a cumulative effect.
Replies
5
Views
380
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top