spud1

-
Arms
Hi everybody,

I have encountered a problem with EFL (Zs) testing a couple of times recently.
I have had unusually high readings for the length of circuit and earthing system type and the increase in impedance seems to be coming from resistance across the line pole of the RCD in the consumer unit?

Has anyone else had this and have any explanation for it? as I am worried about he circuits in question achieving their disconnection times with such high readings!

Thanks
 
I would carry out the EFL test each side of the RCD and compare ,,,


Check all connections , do an RCD test it may be faulty..
 
have had same problem as ray says check incomer of rcd and outcoming side if vastly different then could be loose conection inside rcd and as these have limits that they must meet .if new send it back and they will replace. newlec rcds and megger testers just dont mix. but you still have to meet your 80% values to meet disconnection times
 
have had same problem as ray says check incomer of rcd and outcoming side if vastly different then could be loose conection inside rcd and as these have limits that they must meet .if new send it back and they will replace. newlec rcds and megger testers just dont mix. but you still have to meet your 80% values to meet disconnection times
so..if carrying out a measured value of Zs (he must be for RCDs to be in the equasion)..is this a true statement?
 
Higher Zs test readings than the calculated figure (from R1,R2&Ze), are quite common.
It is a by-product of not tripping the RCD during testing, the tester cannot put a big enough current through the RCD to accurately assess the Zs, so it calculates the result from the low current test it does.
Some testers are better than others, and I believe the Fluke range are the most accurate in this test as they give very short bursts of high current to bypass the RCD tripping problem, and using an higher current give a more accurate reading.

I've experienced a number of different results that were higher than expected, MK were the worst, giving a ~0.50 ohm higher reading. The internal electronics of the RCD also affect the result when using the 'no trip' testing function.
 
the point i`m making is that the 0.8 correction factor is used when Zs is calculated from Ze+(R1 R2)....

- - - Updated - - -

not for measued values of Zs...
 
Then why at my scam inspection do they ask what value do I work to and insist it is the 80% value that I use
I am not disagreeing with you just saying what I have been told to use
 
Then why at my scam inspection do they ask what value do I work to and insist it is the 80% value that I use
I am not disagreeing with you just saying what I have been told to use
because (yet again) they are telling you a load of old cak..
 
remember this:

if a Zs has been acheaved by calculation...that is to say you have taken a Ze...and added (R1 R2)...to get a Zs...then you have added whats refered to as a `hot` and a `cold` value together...and so 0.8 is applied to the tabulated value of Zs to allow for this

for actual measured values of Zs...then it would be the actual measured value that would apply...without the 0.8 correction factor applied
 
Hmm, I think there is a little confusion going on here, or maybe I'm not reading it right?

The max Zs figures are given in BS7671, eg, a 32A CB is 1.44 ohms.
That figure is the maximum Zs for that CB at 70 degrees.See the note at the bottom of the tables.

The figure at room temperature (~20 degrees) must be lower than 1.44, hence the 80% rule of thumb that you apply to your calculated figures and, the measured figures.

There are calculations you can do to find the exact value at various temperatures, but it takes time to do, and with many electricians not having the skills or time to calculate it properly, the OSG gives the 80% figure, that will assume a worst case scenario, and will give plenty of leeway for temperature rises.

So, yes, if it isnt calculated correctly,(using temperture correction factors), the 80% figure is used for both R1+R2+Ze figure, and the measured Zs figure (when taken at ambient temperature).

If your measured / calculated Zs on a 32A circuit is (say) 1.4 ohms at 20 degrees, then it will not comply at 70 degrees, so the OSG 80% figures should be used as the maximum Zs for the majority of electricians, unless you want to calculate using the temperature correction factors, which do give a more accurate result, and can be used to make marginal figures comply, whereas using the 80% may show the circuit to not comply.

Alan.
 
Not what I was taught. if when measuring Zs you were to apply enough current to raise the conductor temperature to 70C then that would be correct. However your mft only gives short bursts of low current, not enough to raise the temperature so you are effectively still measuring at ambient temperature and must apply the correction factor.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
High Earth Fault Loop Impedance readings caused by RCDs
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
spud1,
Last reply from
rattlehead85,
Replies
28
Views
21,868

Advert

Back
Top