Hello all,
I am studying to be an electrician but outside of the classroom I have little experience.
A friend has bought a house and during the buying process had an eicr with unsatisfactory result.
Reading the report it shows the ring and shower circuit to have high earth loop impedance.
I ran the test myself today and the earth loop impedance on the ring and radial are around 40 ohms, which is what the eicr also shows.
I have checked the wiring of all the sockets and all seem to be terminated correctly.
r1, rn and r2 for the ring all seem fine.
According to the report the Ze is also fine.
What could be causing this?
I suspect a problem with one of the other circuits, would I be going down the right alley with that assumption?
Thanks,
Nick