duxter121

Hope someone can help, I am an industrial biased electrician & a friend has asked me to check an outside tap on one of his houses where the tennant keeps getting a belt off the tap, the loop test at the board shown up 17.8ohms & was registered as dangerous on the tester (A Metrel tester)...
The supply I think...is a TT system or a TN-S, not got a regs book with me & not 100% on supply systems (which i'm reading up on now)..bad I know
Anyway, there is 2 cables run down the outside of the house & what looks like the earth is tapped off the neutral about 1 METER before the cut-out & disappears down the wall & under the decking....I do know that he had a dodgy spark do some work on it for him years ago & I have done some reading up on possibilities of what it could be & the only one I can think is that they may have used the other services, gas & water to bond the house
There is no earth at the cut-out or electric meter....
 
You need to ID the earthing arrangement at 17.8 ohms on a TT is acceptable.

However the issue re the water pipe being live needs urgent attention!

IMO your friend needs to call out a spark who can investigate any issues that the dodgy !!!!!spark!!! has left and make them safe ASAP.

Welcome to the forum!!
 
Who is the DNO matey...?? So what would explain the shocks she keeps getting off the outside tap...could it be that its been equip bonded to the mains...?? its an old 15th or 16th edition board with type B MCB's...thanks for the reply too ;-)
 
Sorry mate I easily slip into acronym mode. Distribution Network Operator
The reason for the pipework being live could be a few things, It's a rough way to do it but you could try turning off ther MCBs one by one and hopefully you could identify which circuit is faulted then test the bejaysus out of it to find the problem but it needs to be bottomed out pretty damn quick I'd say
 
its not always live, it wasnt live while i was there & even with running water, did the loop test & wasn't happy with the result hence me panicking a bit after trying to tell the tennant not to worry too much...or should I have told her to worry, I am currently trying to get in contact with the houseowner & doesnt seem to be picking up ...hmm, cheers tony
 
cheers trev & tony... I hate to leave things I dont like & not being that fluent in domestic installations, earthing arrangements etc...(bad I know) I'm not sure what to look for ie, test results from the regs (lent my copy out anyway..!!!)
I am more industrial & commercial....hence me not doing houses...i'm not built for it anyway...ha
 

Reply to High earth loop readings in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top