can anyone out there throw up any ideas as to why i got a high pfc reading of 15.2 ka on a domestic installation??
 
Well there's you answer, it's that chap Ohms again!

Your Zs is probably so low as a result of a low Ze plus parallel paths from protective bonding conductors.

If your consumer unit is to BS60439-3 or BS5486-13 and you have a BS1361 fuse at the DNO supply then you can use 16kA as the short circuit rating of your protective devices.
 
I've never come across a PSC/Ze anything like that on a domestic...are you sure your meter is reading correctly?

Same here.

Mathmatically the numbers make sense, but theoretically, on a domestic, those numbers dont seem plausible.

Is the supply transformer in the basement or something?
 
I tested a caretakers house recently where the DNO transformer was literally in his garden inside a metal cage, that had a rather large PFC too!

Our test meters are pretty poor at measuring such miniscule values of impedance so where accuracy is imperative, a known resistance can be incorporated into the circuit (R2 lead for example) to lift the test meter into it's sweet spot.
Another way is to use the transformer impedance if you can read the rating plate.
 
ive come across this, can you take the 1361 16ka as the max? surely the 6ka 60898s are first to come in to contact with the fault. plus parallel paths surely are removed when testing for ZE. any info on this would really help.
 
ive come across this, can you take the 1361 16ka as the max? surely the 6ka 60898s are first to come in to contact with the fault. plus parallel paths surely are removed when testing for ZE. any info on this would really help.

Check out BS60439-3 UK Annex ZA.

Parallel paths removed for Ze but should be present for Zs at the cu and for PFC
 

Reply to high pfc reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

You would be best checking all connections as it is possible it is having a cumulative effect.
Replies
5
Views
380
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top