Is that the one that states when a BS 1361 type II (33Ka) is the fuse cutout. All MCBs protected by this can be taken as rated as 16Ka?
 
Hi. I know this an old post but have just come across the same problem and the highest reading is 19.9kV. So to comply the breakers MUST be higher than the potential fault current otherwise the breakers will be damaged if they disconnect because of this. Or so I think! Anyone know where the regs say different please? e.g. having read the above posts 434.5.1, is that saying the BS1361 Type II fuse on the supply side (in my case) is sufficiently rated at 33kA that the MCB/RCBOs in the board can be 6kA? Follow?! Help! lol
 
imo 434.5.1is saying that as long as there is discrimination between the fuses

Inverse discrimination really, the upstream device is required to open before the time frame for damage to occur to the mcb (in this case).

The fact that the mcb is actually mechanical means that the simple fuse (on higher fault currents) will operate faster.
 
Thanks for the pointers.
Now the problem is a real mistery...I thought the L port was faulty and this was the reason for the high PFC readings. I thought this as when I used the plug in L probe tester, instead of standard L lead, the PFC were within limts, well under 6kA (using Megger 1552).
Now I have been sent a loan unit because of this problem but when I repeat the test it is exactly the same?!
So using the standard L and E leads the PFC are well outside of limts but when I use the L plug in probe and E standard lead the results are fine?!
Any ideas why this is please? Thanks.
 
I don't know about the differences but I know that at values of less than around 0.5 Ohms, the meters that we generally use are innacurate.

Add this to the difference 0.02/3 of an Ohm can make to PFC and you see where the problems are magnified.

I'll type out my method of measuring Zs close to the supply transformer, it helps to lift the meter into it's accurate 'sweet spot'.
 
Thanks for the pointers.
Now the problem is a real mistery...I thought the L port was faulty and this was the reason for the high PFC readings. I thought this as when I used the plug in L probe tester, instead of standard L lead, the PFC were within limts, well under 6kA (using Megger 1552).
Now I have been sent a loan unit because of this problem but when I repeat the test it is exactly the same?!
So using the standard L and E leads the PFC are well outside of limts but when I use the L plug in probe and E standard lead the results are fine?!
Any ideas why this is please? Thanks.

If you have a 3 probe meter are you using all 3 probes?
 
Hi. The PFC with a megger 1552 is 2 leads only Red (L) and Green (E). So L lead to incoming live and E lead to the earth bar, then the other test is L lead to incoming live and E lead to incoming neutral.
 

Reply to high pfc reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

You would be best checking all connections as it is possible it is having a cumulative effect.
Replies
5
Views
380
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top