OP
SimpleSimon
Is that the one that states when a BS 1361 type II (33Ka) is the fuse cutout. All MCBs protected by this can be taken as rated as 16Ka?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss high pfc reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Is that the one that states when a BS 1361 type II (33Ka) is the fuse cutout. All MCBs protected by this can be taken as rated as 16Ka?
imo 434.5.1is saying that as long as there is discrimination between the fuses
Thanks for the pointers.
Now the problem is a real mistery...I thought the L port was faulty and this was the reason for the high PFC readings. I thought this as when I used the plug in L probe tester, instead of standard L lead, the PFC were within limts, well under 6kA (using Megger 1552).
Now I have been sent a loan unit because of this problem but when I repeat the test it is exactly the same?!
So using the standard L and E leads the PFC are well outside of limts but when I use the L plug in probe and E standard lead the results are fine?!
Any ideas why this is please? Thanks.