Hi everyone. Did a test last week and sorting the paperwork. On the downstairs lighting circuit I got an R1+R2 reading of 3.35 but a Zs of 0.90. Normally I'd go looking for a loose connection somewhere myself but the company I work operates in a way where I've got a limited time to do the inspection and then someone is sent behind me to put anything right. If I add my Ze to that R1+R2 it is within the maximum permitted Zs for the circuit. But to be sure I measured the Zs.
Would you put the higher than expected R1+R2 reading down as a C3 or C2?

Thanks
 
Hi everyone. Did a test last week and sorting the paperwork. On the downstairs lighting circuit I got an R1+R2 reading of 3.35 but a Zs of 0.90. Normally I'd go looking for a loose connection somewhere myself but the company I work operates in a way where I've got a limited time to do the inspection and then someone is sent behind me to put anything right. If I add my Ze to that R1+R2 it is within the maximum permitted Zs for the circuit. But to be sure I measured the Zs.
Would you put the higher than expected R1+R2 reading down as a C3 or C2?

Thanks
You did a test so you just need to report what you found and let whoever comes after you find out why the reading is not as expected, and I think it's an F1 further investigation needed
 
You don't mention what type of property this was, or what type of light.

In a domestic property, you can often roughly tell the order a lighting circuit was wired from the R1+R2 readings. And an unusually high reading will often stand out as being a bit odd. If a ceiling rose, then I'd typically check the connections are tight and remeasure, bearing in might the issue be at the previous fitting.

But it sounds like you are not given time to interpret the results as you test, though one reading quite a lot higher than the others might stand out.

I'd mark it as FI on the EICR.
 
You say downstairs lighting.....house I assume?

It's gonna be 1mm/1mm or 1.5mm/1mm 6242 cable I also assume

How long is circuit approximately?
Depending on temp when tested, but it wont affect it much, based on R1+R2 of 3.35 Ohms, if it was 1mm, your circuit would be 93M long......If it was 1.5mm, it would be 111M long. Not sure how you wired it, can you clarify?

Did you disconnect cpc from main earthing terminal when you tested R1+R2? Have you considered parallel paths with the Zs?
 
I would say the lighting circuit probably has a class 1 light fitting screwed to something that's bonded. You can't exclude that from the live tests, that's why the dead test is the gold standard.
 

Reply to High R1+R2 but acceptable Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
265

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top