hello, just started in this game and am currently dead testing some lighting radials made of gu10 and low voltage emergencys, the R1+R2 readings are a bit high in comparison to table 11 appendix 1 in the osg. Is this the transformer packs causing this? Also am i right in thinking to disconnect the said transformer packs for insulation as pushing 500v through them could damage them? If any experianced sparks could give me some valuable imformation it would be much appreciated before i start pulliong every lamp down and making a mess of the ceiling to check connections etc.
 
What do you mean by 'a bit high'. What do you think it should be?
And what is the actual ? Shouldn't affect R1+R2, if doing correctly. Link L and N and IR test to earth.
 
Last edited:
yes shorting line and cpc at db and testing switch line and cpc on last lamp in radial, there is one or two emergencys in place of gu10s throughout the circuit and the conductors are hard to access now as job is near completion (no pressure lol) hence i dont want to start pulling the ceiling down.
 
If it is not practicable to remove loads for IR testing, then as ipf says, link L-N and test to earth with switch on, and L-N with switch off to test as much wiring as you can. Yes, you would have to remove transformers and lamps if you are doing L-N IR test.
 
not my design but yes i believe everything is good and meets the requirements from the visual point of view, its not my install so just trouble shooting as to why the continuity reading is a bit high? just asking for some experienced help as obviously i want the circuit to be safe.
 
no just a single switch for each circuit i will need to get the installer to re trace his circuit and see how accurate his pacing is i think lol!
 

Reply to high R1+R2 on radial lighting with emergencys in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
449

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top