Is this a Eicr or an initial verification ? its not clear to me which one you are carrying out


The insulation resistance test can be modified to suit which role you are involved with

If its initial, then the test should be before the transformers are fitted,if its a report,then L and N can be linked together and tested to earth

Why are you sure of the length the circuit should be compared to the actual length,how do you know the actual length ?
Who is the test for if its not your design ?

I don't understand what your role is to make any comment on the R1+R2

 
If you are measuring a cable of known length at 20 degrees C then the value should be 1.5ohms.
Once you have multiple junctions in the cable and the cable may take various routes and not be exactly 50m then you could easily get 1ohm difference; it is likely to comply with the max Zs requirements.
 
thank you everyone for your help and responses, i discovered there is a seperate feed to the emergencys as it was done with 2 core and the installer ran an extre line in, problem solved thank you.
 
If you are measuring a cable of known length at 20 degrees C then the value should be 1.5ohms.
Once you have multiple junctions in the cable and the cable may take various routes and not be exactly 50m then you could easily get 1ohm difference; it is likely to comply with the max Zs requirements.
yes and this is why TDRs arnt really any good for fixed installs richard.....cables taking different routes....
 
I use lightmates so used to taking the lamp out whenever possible. Should have said "...then testing at load end" . Apologies :)
i use lightmates as well guitarist...for R1 R2 and Zs....so if its open circuit at the lampholder on an R1 R2...if a BC type then just turn it through 180 degrees....if an ES..then its further investigation (3)...and will come back as wrong polarity on loop....so the same for Zs....:wink:
 
On new installs I often get high readings caused by switch resistance. Flicking the switch a few times usually produces an acceptable figure.
 

Reply to high R1+R2 on radial lighting with emergencys in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
449

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top