High R1 + R2 reading... | on ElectriciansForums
Discuss High R1 + R2 reading... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
sambuca2907
Could I pick someone's brains with this - as I've been scratching my head trying to think about it!
I've got a 25 metre 2.5 SWA run to a garage, running 2 double 13A sockets as a radial. Protected by a 20A MCB on an RCD (17th regs compliant), located in the house CU.
Customer asked me to re-do the lights in the garage - and to save running a new supply I've put in a 5A spur from the garage radial (BEFORE the sockets).
From this I've got 2 way switching - in 1mm 3&Earth,
and 2 F.L. Tubes, ran in 1.5mm T&E.
Gone to test the install - and got an R1 + R2 at the furthest light at 2.03 Ohms! Thought this was really high so checked all connections and re-tested - same result... Checked the R1 + R2 at the sockets and got around 0.65 Ohms - much more realistic figure! Is this just simply because of the amounts of 1mm and 1.5mm I've used in the 2-way lighting?? When I obtained the figure I disconnected the F.L. Lights, just incase they were effecting the result.
With the Ze being 0.14 Ohms, this makes the Zs 2.17. However the circuit is protected by RCD - and the RCD trip times are within limits (34.8 ms @ I and 12.5ms @ 5I)
Try disconnecting your spur and joining your cables in a block connector.
The fuse in the spur unit might be giving you a high reading.
Approx R1 + R2 values for 1.5mm T&E are 0.29 ohms / 10 meter run.
1.0mm T&E 0.38 ohms / 10 meter run.
Reply to High R1 + R2 reading... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
6K