TestEngineer

I have an installation (TN-S system) and the Ze measure is 3,89Ohms.The start point of the installation protected by ELCB 500mA.Some final circuits protected by rcbo 30mA and the rest by mcb.I suggested to the client the replacement of the feed cable but for economic reasons this will be late for one year.My question is if the installation is safe as above and if no please give me proposed solutions.

Thanks
 
As the DNO are under a duty to maintain any earth they provide I'd say a call to them is in order. Because it's so far above the max allowed in 7671 they should come fairly quickly. Are you sure it's a TN-S though mate? We've seen a few diy mofidications on here
 
Is that 3.89 ohms ? How old is the installation?

Trev quite rightly on both counts posted that if the DNO have supplied an earth they have a duty of care to maintain it, and that would be my firsr call to see if they had supplied it.

Over the years as he rightly pointed out Sparks have often done DIY TN-S systems without the DNO knowledge, if this is the case then you might have to either pay to have the system made into a TNC-S or if it's not available make the system TT.

As for existing with an upfront 500mA ELCB ( Voltage or Current?) and then 30mA additional protection I should imagine the installation is safe. I would though test the operating times of these devices
 
Last edited:
In the past, DNOs would install up front ELCBs where they were no longer able to maintain the earth.
I believe the practice nowadays is just to tell the customer to TT the installation.
Once installed, the ELCB became the responsibility of the customer.
 

Reply to High value Ze in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
709
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top