I'll start with the problem.

I've installed two Hive Mini Pro 3 EV chargers, and both have had the same fault, which I think I've now isolated to the CT Cable (Not the clamp or its direction).

Essentially if I connect the CT Cable to the EV Charger and enable smart charging, the EV Charger will randomly report an earth fault. If I disconnect the CT Cable and disable smart charging, the EV Charger works perfectly fine.

I have extended the CT Cable provided with the clamp, in the same way at both installations using a Doncaster EV Ultra Cable which contains a shielded CAT 5e cable. Then connected one twisted pair to the CT Clamp Cable using Wago's, the other end of the twisted pair to the EV Charger.

The install instructions for the Hive does suggest that if a shielded data cable is used the sheath needs to be earthed, but I can't work out how.

Has anyone else have experience of the Hive Mini Pro 3 chargers, and if so have you come across a similar problem. How did you extend the CT Clamp cable if you needed to ?
 

Reply to Correct Method to extend CT Clamp cable for EV Charger (Also should it be earthed) in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
714
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Agreed, loss of N further down the network can give wildly changeable voltages If it is tied to earth, then that will go up and down too.
Replies
3
Views
414
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top