Urgent advice please.

I have done a consumer unit change where the main earth is 10mm and meter tails are 16mm.
I have connected new 25mm tails on consumer side of isolator switch and 16mm main earth to single pole block onto DNO 10mm earth.

Problem I have is a Ze of 0.54 and PSCC of 10KA. Is this something I can correct or is it a DNO problem?

Zs on all circuits is within limit except oven circuit which is 1.52 against max permitted 1.44.
Obviously will come down if Ze does.
 
can you lower the breaker at all?

Not sure of the cooker rating. Very old free standing unit.
6mm T/E used from 32A breaker and cooker switch has a socket.

Would lowering to 16A create tripping problems ??

Long term the Client has sumitted plans to extend property and the kitchen will be moved with new circuits and appliances.
 
depending on make of board, you can order 25 amp MCB,s, alternatively if you cant get one to fit the board you could put an enclosure next to the consumer unit and down rate it slightly, that is if the cokker loading allows
 
Well, if you go by the regs then you would be ok as the CU you have just installed will have full RCD protection, which allows 1667 ohms.

Thanks Jason.
17th ed high integrity cu fitted.
With the intended plans to extend and relocate kitchen etc. Is it enough to just comment on the high reading on the cert and leave it at that. ?
 
depending on make of board, you can order 25 amp MCB,s, alternatively if you cant get one to fit the board you could put an enclosure next to the consumer unit and down rate it slightly, that is if the cokker loading allows

An additional enclosure next to cu not really an option as just fitted 17th ed high integrity 15 way board to allow for all future build plans on property at client request to avoid all seperate enclosures and add ons etc. Do wylex do 25A
 
Thanks Jason.
17th ed high integrity cu fitted.
With the intended plans to extend and relocate kitchen etc. Is it enough to just comment on the high reading on the cert and leave it at that. ?

Yes you can and i expect you will need to include the cost of a new radial for the cooker when the other works are being done.
 

Reply to High ze and circuit zs ???? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
323
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
851
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top