Urgent advice please.

I have done a consumer unit change where the main earth is 10mm and meter tails are 16mm.
I have connected new 25mm tails on consumer side of isolator switch and 16mm main earth to single pole block onto DNO 10mm earth.

Problem I have is a Ze of 0.54 and PSCC of 10KA. Is this something I can correct or is it a DNO problem?

Zs on all circuits is within limit except oven circuit which is 1.52 against max permitted 1.44.
Obviously will come down if Ze does.
 
So your R1+R2 on a cooker circuit is nearly a whole ohm?!

What CSA is the cable, and how long is the run?

Yep 0.98
6mm t/e and only about 5 or 6m to the cooker switch which is within 2m to cooker outlet.

Possible poor connection but switch tiled in many moons ago and cooker not been moved for years either. Will need to pull both out to check.
 
6M of 6.0/2.5T+E, should have an R1+R2 of 0.062ohms.....you have something very wrong there methinks.

Is your test equipment working properly???

Fluke tester just back from calibration 2 days before.
Tested circuit 2 or 3 times and got same reading.

Will check all connections on circuit and leads on tester and test again I think.
 
If the R1+R2 and Zs are correlating, then I would think that it's not a problem with the meter, but more the fact that you have a relatively high resistance joint somewhere in the cable run.

Putting an RCD would allow it to trip out in the required time in the event of an earth fault, but this would be just covering up a much more serious fault that appears to be a dodgy joint could possibly cause a fire through arcing.
 
...... but this would be just covering up a much more serious fault that appears to be a dodgy joint could possibly cause a fire through arcing.

I would have thought that if it was going to catch fire through a bad joint, then it would have by now.

But of course, thats not to say that it never will, so i would tend to agree.
 

Reply to High ze and circuit zs ???? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
323
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
851
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top