Hi all,

Been testing on part of the motorway network and come across a few Ze readings which are a little higher than should be for a TNCS supply. Getting 0.45 Ohms from one supply and 0.51 from another.

Been told that the DNO will just state that 0.35Ohms is a guide and that they wont bother their arses to look into it? Is this really the case? Going to give the DNO a call in the morning and hopefully get them to raise a job so they can attend, was just wondering of anyone has had any similar experiences.

Also, If for example, the main cut-out is a BS1361 100Amp, but my Zs at the dist point is higher than the maximum Zs stated in BS7671, am I ok to replace the fuse for a lower rating or again, is this a DNO job?

Many Thanks
 
they should sort out the high Ze. your max Zs is dependent on the circuit ocpd, not the cut-out fuse, assuming the circuit is fused down,
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High Ze and Zs at PDU.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
1

Thread Tags

Tags Tags
pdu

Advert

Thread statistics

Created
sharpy1983,
Last reply from
telectrix,
Replies
1
Views
1,003

Advert

Back
Top